#90721 - 12/08/04 06:37 PM Bathroom circuits  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
If I have 4 bath rooms in a single dwelling dont they all have to have their own 20A circuit?

You can not feed the lights or fans or any other room from this circuit either right?

thanks for any replies..

-regards

Mustang


Electricity has no respect for ignorance!

2017 / 2014 NEC & Related Books and Study Guides

#90722 - 12/08/04 07:08 PM Re: Bathroom circuits  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
You have a choice: 1) A single 20 amp circuit for all four (or more) receptacles in the four bathrooms, and the lights, fans, etc wired from a separate lighting circuit, which may include other rooms. 2) Four 20 amp circuits, one dedicated for each bathroom, including the lights, fan and maybe even a heater, too, if there is sufficient capacity. 3) A separate 20 amp circuit for each receptacle in each bathroom, with the lights and fan on any lighting circuit. 4) Two receptacles from two bathrooms on a single 20 amp circuit, 5) combinations of 3 and 4.
220.14(J) makes it clear these outlets are included in the residential general lighting load, and therefore are unlimited in the number allowed per circuit.


Earl

#90723 - 12/09/04 07:48 AM Re: Bathroom circuits  
Megawatt  Offline
Member
Joined: Mar 2004
Posts: 76
Lexington,Ky, USA
I find it best to run the Home Run to the GFI receptacle, & feed the lights, fans etc off the load side.
That way everything in the Bathroom is GFI protected !


#90724 - 12/10/04 09:37 PM Re: Bathroom circuits  
Speedy Petey  Offline
Member
Joined: Aug 2003
Posts: 173
Upstate, NY
And when the GFI trips from all the moisture you can slip and fall in the dark.


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein


Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7595 MB (Peak: 0.8910 MB) Zlib enabled. Server Time: 2017-04-28 06:12:44 UTC