#90198 - 11/02/04 09:10 PM Derating Application  
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
We had one of our crews run into a situation yesterday with derating.

Final inspection, a new office in a converted industrial space. The guys had run 7 ckts. in a 3/4" emt. 7 hots, 7 neutrals, one ground, #12 thhn, 20a ocpd.

The state inspector failed them for derating. He said that, "Since this was a single phase service all neutrals are counted as current carrying conductors." These circuits are all general use plugs and lighting. No Non-linear loads, no HID lighting.

My repsonse is WTF??????? This is definitely a new one on me. I consider that conduit to have 7 current carrying conductors per the NEC. Please educate me if I'm wrong.

GJ


2017 / 2014 NEC & Related Books and Study Guides

#90199 - 11/02/04 09:16 PM Re: Derating Application  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I don't know how other guys figure this, but I'm pretty sure if I took the neutral out of the service and pinched it's end between my fingers, then, with a different finger, touched the screw where it came from I'd find it to be "current-carrying", so I count it as such.

(Don't try this at home.)

Dave

[This message has been edited by Dave55 (edited 11-02-2004).]


#90200 - 11/02/04 10:39 PM Re: Derating Application  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
Current may indeed flow through your fingers but I dare say it would be "unbalanced current" and thus 310.15(B)(4)(a)would apply, no?

310.15(B)(4)(a)
A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions
of 310.15(B)(2)(a). (derating table)


#90201 - 11/02/04 10:48 PM Re: Derating Application  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I understand that portion of the NEC to apply to multiwire branch circuits. As it is described as 7 hots and 7 neutrals for 7 circuits, I don't think it applies.

Dave


#90202 - 11/02/04 10:56 PM Re: Derating Application  
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
Junkie,
I'm under the impression that you have 7 two wire circuits which means they are all current carrying conductors. Looking at 310.15(B)(2)(a) you find that you must derate to 50% of the thhn value of 30A and the ocpd would be 15A.
Why aren't you installing 3 wire circuits which would reqire you to derate to 70% and your ocpd would be 20A?
Ron


#90203 - 11/02/04 11:19 PM Re: Derating Application  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
You guys are right. I was thinking 3 wire circuits with shared neutral. Separate neutral with each phase wire - all neutrals are indeed current carrying conductors.


#90204 - 11/02/04 11:21 PM Re: Derating Application  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Nailed on derating, and fill factor.

358.22 to Chapter 9 Table 1, and notes to Tables. 40% fill, not 88%.

The only way I could see 15 #12's being allowed, is if were in a 23" conduit, and even then, I wouldn't do it.



[This message has been edited by e57 (edited 11-02-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

#90205 - 11/02/04 11:36 PM Re: Derating Application  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I use Annex C, Table C1 Maximum Number of Conductors....in EMT.

Type THHN, THWN for 3/4" EMT is 16 conductors for 12 ga. Of course there would be some derating involved.

Dave


#90206 - 11/02/04 11:42 PM Re: Derating Application  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
Up to 16 THHN conductors in 3/4" EMT allowed per table C1 in annex C.


#90207 - 11/03/04 12:06 AM Re: Derating Application  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Mark,
The tables in Annex C are not 100% fill, they are based on Chapter 9 Table 1. (16) #12 THHN conductors would meet the 40% fill requirement for ¾” EMT according to Annex C Table C1.
The area of #12 THHN is .0133”
16 X .0133 = .2128”
¾” EMT is .213 @ 40% fill

Curt


Curt Swartz

Page 1 of 3 1 2 3

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.8176 MB (Peak: 0.9924 MB) Zlib enabled. Server Time: 2017-07-23 08:43:54 UTC