#89991 - 10/26/04 11:08 PM UF Cable Under Pool Apron  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Any restrictions on installing UF cable under a pool apron? Not under the pool itself.

Looking at running switch legs under 6 inch apron around pool.

Feeder from sub panel on side of house will be in PVC...insulated ground and neutral..#8 from pool steel and it is insulated...did see that the pool guy just wrapped the wire under a nut on a 3/8 stud..that did not look too good but i am not doing that part..just tieing in the ground from the pool steel to the egc from the sub..any prob with that?

i thought i read somewhere that any runs under a pool had to be in conduit..my memory aint what it used to be..

thanks for any replies...

-regards

Mustang


Electricity has no respect for ignorance!

2017 / 2014 NEC & Related Books and Study Guides

#89992 - 10/26/04 11:27 PM Re: UF Cable Under Pool Apron  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
I can't speak for the code, but...

I advise against it, because I currently have a customer whose pool apron covers a bad wire run. Since UF was used, replacing this wire is almost impossible to replace this wire, without tearing up the apron.
Also, im my experience, trenches are NEVER deep enough, and UF is almost always run way too shallow.
Run pipe, then transition in a ground box once past the apron area.


#89993 - 10/26/04 11:28 PM Re: UF Cable Under Pool Apron  
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
Mustang,
Where do these switchlegs go??

AFAIK there is nothing that would keep you from putting UF under a pool deck. However, I don't think I'd go that route unless there was no other option. It definitely would be better to go with pvc conduit.


#89994 - 10/26/04 11:37 PM Re: UF Cable Under Pool Apron  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Thanks for the reply. I think you are right and I will go ahead and do this whole job in pvc.

the switches will be controlling the wet niche lighting and 4 coach lights fed from a gfi..

i can easily justify the cost difference..

thanks for taking the time to reply..

-regards

mustang


Electricity has no respect for ignorance!

#89995 - 10/27/04 01:57 AM Re: UF Cable Under Pool Apron  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
You are also supposed to be 5' from the pool if space is available 680.10


Greg Fretwell


Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7668 MB (Peak: 0.9052 MB) Zlib enabled. Server Time: 2017-04-23 10:04:11 UTC