ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Dimmable LED 2x4 lay in fixtures
by HotLine1. 04/24/17 05:43 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,703 Are you busy
169,444 Re: Forum
162,757 Need opinion
Who's Online Now
0 registered members (), 53 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#89883 - 10/22/04 02:50 PM Water Heater Load Calc  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Do I just count the first water heater or the first 1500W of a system with 2 water heaters on line?

Load analysis on plans shows 1500 W and DF of 1.0 which gives a load of 1500W but the load shown on the panel schedule is 2 water heaters using 1750 each leg of 208 single phase service..

i think the plans are wrong..

thanks for any replies.

-regards

Mustang

[This message has been edited by mustangelectric (edited 10-22-2004).]


Electricity has no respect for ignorance!

2017 / 2014 NEC & Related Books and Study Guides

#89884 - 10/22/04 08:39 PM Re: Water Heater Load Calc  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Hi Mustangelectric;

From what is described, it appears the Load calcs for the 2 Water Heaters were figured as Non-Coincidental Loads (is this possible?), and the Nameplate rating of the higher load (in this case both loads are equally listed as 1500 Watts @ 208 VAC), is figured at 100%, where the usual load is expected to be continuous at full Nameplate rating
(I think this would be found in Table 220-30 of the '99 NEC, or possibly the '96 NEC... not sure, but I do remember it under Optional Calcs section of Article 220, and pertains to Electric Thermal Storage Equipment).

If this is the case, then it would be permissible to do the Load Calculation for the Water Heaters this way, and compile the data to the complete Service / Feeder Load Summary.

The Panel Schedule will reflect the actual Loads of each Circuit, normally in Volt-Amp values, and will include an LCL adder for Continuous Loads - whereas the LCL may not be included within the Load Summary, as described above.

A debate could be made regarding if a Water Heater - under normal operating circumstances - would be a Continuous Load or not.
Would one (or could one) draw the rated 1500 VA for 180 minutes and longer?
I used to view them as Non-LCL, until reality clicked in; whereas a Storage Tank Water Heater may easily - either by intentional use or mistake / accident - be drawing Nameplate rating for 3 Hours and above.
One scenario would be high capacity Tanks, and the usage was intentional, such as:
<OL TYPE=1>

[*]20 minutes of Hot Water use to wash dishes,


[*] Immediately afterwards, someone takes a 20 minute shower,


[*] Another person fills up a Bath Tub after person finishes shower,


[*] Washing Machine is kicked in, doing extra large load and warm water use,


[*] etc....
</OL>
All these instances occuring one after another, barely giving the storage tank enough time to actually store hot water.

As for the mistake / accidental scenario, someone leaves the hot water running and just takes off (short term memory problem, I would guess!), leaving the water flowing until someone notices it and puts a stop to the rampant waste.
This could also be from an accidential situation, where hot water pipes failed and began leaking massive amounts of hot water.
Mr. Gopher and Mr. Rat may have chewed through the pipe, causing a leak, or they may have knocked over something (coupled with a "Domino-Effect" like falling of objects), which caused considerable damage to the hot water pipe(s), therefore allowing near-full volume output until someone comes along to end the chaos.

Now looking at the Panel Schedule's listed Load of 1750 VA, this falls short of what the rated 1500 VA Load + LCL should actually be!
It would be 1875 VA listed in the Cells of the Panel Schedule for the Water Heater Circuits.
Example:
Water Heater #1... let's say Circuits 18/20;
&#216;A Cell = 1875 VA for Circuit 18,
&#216;B Cell = 1875 VA for Circuit 20.

Water Heater #2... let's say Circuits 25/27;
&#216;A Cell = 1875 VA for Circuit 25,
&#216;B Cell = 1875 VA for Circuit 27.

Not sure where the 1750 came from, as it would be 116.667% of the rated load VA. Anyone know whazzup with this?
Kind of looks like a "Guesstamation" thing to me... [Linked Image]

BTW, feel free to substitute Watts for Volt-Amps in this case - since the Load is very much pure Resistance. I am "Programmed" to view Loads as Volt-Amps, especially when Panel Schedules are described!
Not that it is correct, only that it's default to me. Trying to go against this train of thought results in "Mental Blue Screens" and Logical Paradox problems, which requires someone to manually restart me. ....
[Linked Image]

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!


Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.003s) Memory: 0.7479 MB (Peak: 0.8665 MB) Zlib enabled. Server Time: 2017-04-26 04:02:10 UTC