#89742 - 10/17/04 12:45 PM Ground Rod  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
What are the required dimensions for a galvanized steel rod if it is to be used as a gounding electrode? Trick question.


George Little

2017 / 2014 NEC & Related Books and Study Guides

#89743 - 10/17/04 12:50 PM Re: Ground Rod  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I will take a swing at this.

5/8" x 8' minimum.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#89744 - 10/17/04 12:55 PM Re: Ground Rod  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
Ah the new Galvan Electric rod huh?

If U/L is OK with it I am OK with it ... until someone tells me otherwise.


Greg Fretwell

#89745 - 10/17/04 01:13 PM Re: Ground Rod  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I agree with Bob.


Ryan Jackson,
Salt Lake City

#89746 - 10/17/04 01:13 PM Re: Ground Rod  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Wouldn't we have to wait for 250.52(A)(5)(b) to get changed?

Quote
250.52(A)(5)(b)Electrodes of rods of iron or steel shall be at least 15.87 mm (5/8 in.) in diameter. Stainless steel rods less than 16 mm (5/8 in.) in diameter, nonferrous rods, or their equivalent shall be listed and shall not be less than 13 mm (1/2 in.) in diameter.


In my mind a galvanized steel rod is not equivalent to Stainless steel or nonferrous rods.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#89747 - 10/17/04 01:29 PM Re: Ground Rod  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Boy, you guys are right on top of your game. Yes it is all about the Galvan Electric rod. 250.25(A)(5)(b) is kinda poorly written (surprise, surprise) and hopefully it will get re-written someday. In talking with NEMA rep. they use the word "nominal" meaning something in name only when talking about a 5/8 ground rod. Actual dimensions are considerably less than 5/8". The Galvan rod is also less than 5/8" but it has the blessing of UL and I am not sure but maybe we should lean towards using this listed product rather than using and approving the "nominal" 5/8" rod.


George Little

#89748 - 10/17/04 02:16 PM Re: Ground Rod  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I remember the last time this rod was talked about, and the site like had a whole "justification" page about thier listing, and sizing.
http://www.galvanizersonline.com/electrical/faq.asp

George, do you have stock in this company? [Linked Image] I don't get the reason why this would be better than a "regular rod"?


Mark Heller
"Well - I oughta....." -Jackie Gleason

#89749 - 10/17/04 02:26 PM Re: Ground Rod  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
From their site.

Quote
What does the NEC Code say about ground rod electrode diameters?

Diameters must be 0.625 inches minimum and the rod length must be 96 inches (8 feet) minimum. Any rod less than 0.625 inches DOES NOT meet the NEC Code, unless it is “listed.” Galvan has achieved this compliance!


What I don't understand is the compliance with "equivalent to Stainless steel or nonferrous rods."

Who decided a galvanized rod is equivalent and if it is what type of rod would not be equivalent?


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#89750 - 10/17/04 02:34 PM Re: Ground Rod  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
This reminds me of the question, "What is the inside diameter of 1/2" conduit?" [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy

#89751 - 10/17/04 03:36 PM Re: Ground Rod  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
To answer e57, I don't have stock in Galvan, wish I did. This question came up at one of our local inspector forums and got us all talking. I have invited the rep for Galvan to our IAEI Annual Michigan Chapter meeting in December and gave him a 15 minute part on the program to clear up the matter. Somehow I doubt 15 minutes will get it.


George Little

Page 1 of 2 1 2

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,457