ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
MRI LED lights dimmer control replacement - wow!
by ghost307. 01/19/18 11:37 AM
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
FPE in Germany
by HotLine1. 01/17/18 07:07 PM
VDE 0100 to introduce AFCIs
by LongRunner. 01/17/18 10:32 AM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
1 registered members (Troy), 20 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Building Steel GEC or Water Pipe GEC? #89653
10/12/04 04:20 PM
10/12/04 04:20 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Is connecting the gec to building steel on a commercial job accpetable versus cold water bond?

it seems to me that you need both but parallel paths could be an issue.

i am looking at a riser diagram that calls for 3 3/4"X8' ground rods placed 10 feet apart and instructions to connect to building steel where possible..

it seems to me that you need a building steel connection and you need a cold water bond..200A service requires a #6 AWG GEC to a made electrode..and a #4 AWG GEC to cold water..correct?

thanks

mustang

thanks for any replies.


Electricity has no respect for ignorance!
2017 / 2014 NEC & Related Books and Study Guides
Re: Building Steel GEC or Water Pipe GEC? #89654
10/12/04 05:05 PM
10/12/04 05:05 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
You must use all available electrodes. See 250.50

As far as the sizing goes, yes, you are correct.


Ryan Jackson,
Salt Lake City
Re: Building Steel GEC or Water Pipe GEC? #89655
10/12/04 05:07 PM
10/12/04 05:07 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
250-50 says if available bond every thing together. sizes look good. #4 also to the steel.
Ryan you beat me [Linked Image]

[This message has been edited by trekkie76 (edited 10-12-2004).]

Re: Building Steel GEC or Water Pipe GEC? #89656
10/12/04 06:22 PM
10/12/04 06:22 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
so you are saying that there SHOULD be a cold water bond IF AVAILABLE?

i am asking because i am working from a set of plans that just ask to bond to three 3/4 X 8' ground rods and to the building steel. the building has copper piping installed. i always bond the copper at the point of entry into the building or first accessible loc

should i make a revision on the dwgs and call for a COLD WATER BOND using a #4 AWG? and should I revise the dwgs to call for a #4 AWG to the ground rods and the building steel? I though #6 was good for MADE ELECTRODES?

sorry if this is elementary to you...grounding is the most important part of any electrical system and it is one of the FUZZIEST too!

i am big on grounding!

thanks

mustang


Electricity has no respect for ignorance!
Re: Building Steel GEC or Water Pipe GEC? #89657
10/12/04 06:35 PM
10/12/04 06:35 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
This may help

[Linked Image]

The engineer is free to ask for more than code minimums.

The Power company around here asks for 4/0 to 3/4" 10' ground rods at transformer pads.

The NEC would say 6 AWG would be enough.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Building Steel GEC or Water Pipe GEC? #89658
10/12/04 06:36 PM
10/12/04 06:36 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Yes, if it is there and meets the description of an electrode, you must bond it with (in your case) a #4.


Ryan Jackson,
Salt Lake City
Re: Building Steel GEC or Water Pipe GEC? #89659
10/12/04 07:46 PM
10/12/04 07:46 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
yes that slide clearly shows the best means to accomplish a proper grounding system

That looks like the same slide on the first page of the NEC handbook

and thanks for the follow up comments regarding the #4

thank you very much!

mustang



[This message has been edited by mustangelectric (edited 10-13-2004).]


Electricity has no respect for ignorance!
Re: Building Steel GEC or Water Pipe GEC? #89660
10/13/04 09:33 AM
10/13/04 09:33 AM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
are the articles:

GEC:250.66
Bonding Jumper: 250.122

regards

mustang

[This message has been edited by mustangelectric (edited 10-13-2004).]


Electricity has no respect for ignorance!
Re: Building Steel GEC or Water Pipe GEC? #89661
10/13/04 09:51 AM
10/13/04 09:51 AM
E
eprice  Offline
Member
Joined: Aug 2003
Posts: 64
North Logan, Utah, USA
Quote
are the articles:
GEC:250.66
Bonding Jumper: 250.122


No, when we're talking about bonding jumpers within the grounding electrode system, they are also sized according to 250.66. (see 250.53(C))

Re: Building Steel GEC or Water Pipe GEC? #89662
10/13/04 04:29 PM
10/13/04 04:29 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
to the made electrodes does only have to be #6. I was talking about to the steel being #4

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,552 Are you busy
180,359 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 1.0236 MB (Peak: 1.1993 MB) Zlib enabled. Server Time: 2018-01-19 19:23:42 UTC