romex from the 1960's #89614
10/10/04 06:34 AM
10/10/04 06:34 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
I want to upgrade the plugs to ground type in a house built in the 1960's.The old romex has a reduced size (#16 I think)grounding conductor in the cable that is wraped around the romex and pinched in the connector or under the clamp of the metal box.
What is the correct way to convert to ground type plugs in this case?
Is the reduced size ground wire in the romex OK to use for grounding?

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: romex from the 1960's #89615
10/10/04 07:20 AM
10/10/04 07:20 AM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
There is nothing wrong with the reduced size grounding conductors. The reason the grounding conductors were required to be made to match the circuit conductors in the smaller cables (#10, #12, and #14) is that too many DIYs and jacklegs were using the grounding conductors for circuit conductors. I have even seen the grounding conductor used as a phase conductor where a single-phase switch was converted to a three way without replacing the cable (they just taped up the grounding conductor and connected it to the switch and light fixture).

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: romex from the 1960's #89616
10/10/04 10:12 AM
10/10/04 10:12 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
Table 250.122 requires a #14 copper grounding conductor for a 15 amp overcurrent device protected circuit...so how can the #16 grounding conducter in the old romex be used for grounding when upgrading a house to grounded plugs?Is there an exception somewhere?

shortcircuit

Re: romex from the 1960's #89617
10/10/04 10:27 AM
10/10/04 10:27 AM
J
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Wouldn't the existing ground conductor be considered grandfather in? It met exisitng codes at time of install.

Re: romex from the 1960's #89618
10/10/04 10:40 AM
10/10/04 10:40 AM
C
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
shortcircuit, If you are doing this in MA check 406.3(D)(3)(b). 250.130 (C) is not acceptable under MEC.

Re: romex from the 1960's #89619
10/10/04 10:45 AM
10/10/04 10:45 AM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
Charlie, I was taught the reason the grounding conductors size was increased was for fault clearing, that is, to prevent the grounding conductor from burning open before the OCPD opens.

Re: romex from the 1960's #89620
10/10/04 11:38 AM
10/10/04 11:38 AM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
BigB, the smaller wire works just fine for fault clearing the same as smaller wire works for fault clearing on larger circuits. Remember that the fault will be cleared before the current will destroy the grounding conductor or table 250.122 would not be valid.

Depending upon where you are working, you may or may not be "grandfathered". You need to check with your local laws and ordinances. In Indiana, you are permitted to continue to wire an addition with the Code that was in force when the home was built. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: romex from the 1960's #89621
10/11/04 11:43 PM
10/11/04 11:43 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Table 250.122 has full size grounds for circuits 15 - 30A!

15=14
20=12
30=10

But I too believe it should be OK as an existing installation. Just check with the AHJ, to be sure. If not, GFCI them!


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: romex from the 1960's #89622
10/12/04 12:14 AM
10/12/04 12:14 AM
N
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 876
If it met the code in effect at the time of installation shouldnt it be Grandfathered in?I was always under the impression that the code was not retroactive but, assuming things can cause lots of trouble.

Re: romex from the 1960's #89623
10/12/04 05:42 AM
10/12/04 05:42 AM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Quote
Table 250.122 has full size grounds for circuits 15 - 30A!
E57, I understand that, please read my first post and then my second post. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,515 Are you busy
180,312 Re: Forum
170,808 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.048s Queries: 15 (0.033s) Memory: 1.0226 MB (Peak: 1.1993 MB) Zlib enabled. Server Time: 2018-01-17 03:34:05 UTC