Busway feeding entire building #89533
09/25/04 06:19 PM
09/25/04 06:19 PM
A
Active 1  Offline OP
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
I was at a small factory about 10,000 sf the other day and noticed something that did not look right to me.

There were 2 services because the bilding was devided in the past. Both 400 amp 3 phase. They each went into a 400 amp Disco and then straight to a bussway maybe 70' long. Off the 2 bussways fed the entire building. Maybe 6-8 panels in different locations 200 and 100 amp were run off the bussway. From those panels it must have fed the lighting, front office, HVAC, and general outlets. They also had the factory machines and a step up transformer off the same duct.

I looked in the NEC and could not find any violations with this. What's your opinion on this. Acceptibale or unaccepticable?

Tom

2017 / 2014 NEC & Related Books and Study Guides
Re: Busway feeding entire building #89534
09/25/04 07:12 PM
09/25/04 07:12 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Regarding the bus duct, I can't think of anything wrong here. This is a very flexible means of distributing power, kind of expensive, but if the power requirements change on a regular basis, might end up being the least expensive way of doing things.


Few things are harder to put up with than the annoyance of a good example.
Re: Busway feeding entire building #89535
09/27/04 05:03 AM
09/27/04 05:03 AM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
This is a common way of feeding high rise office buildings. Come out of the service gear with 4000A bus duct and run it vertical through the electric rooms. Each room has a place to set a couple of disconnects on the bus to feed the floor. From what you describe I see nothing wrong.

Re: Busway feeding entire building #89536
09/27/04 04:22 PM
09/27/04 04:22 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
so, how much DOES a bus weigh? [Linked Image]

Re: Busway feeding entire building #89537
09/27/04 04:26 PM
09/27/04 04:26 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
A lot when you are on the other end of the rope hauling them up the elevator shaft. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9670 MB (Peak: 1.1044 MB) Zlib enabled. Server Time: 2018-01-22 20:12:53 UTC