GEC #89326
09/09/04 09:32 PM
09/09/04 09:32 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Is there ever a time where a MAIN PANELBOARD for a Sinfgle Fam Dwelling would NOT have a #4 bare ground for cold water ground? copper piping.

here in Arkansas the GEC goes from the Ground rod to the METER BASE. In Kentucky it is from the Panelboard to the Ground Rod. If there is a copper water line, you need a COLD WATER BOND..usually a #6 for 100A and #4 for 200A this ALWAYS goes to the MAIN PANELBOARD..

i saw a house today that only had a gec from the main disc at the meter..no other ground in the panel..

this looked wrong to me..

the feed was a 4 conductor SER type cable..

thanks for any replies..

mustang


Electricity has no respect for ignorance!
2017 / 2014 NEC & Related Books and Study Guides
Re: GEC #89327
09/09/04 09:51 PM
09/09/04 09:51 PM
D
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
Allways check with the AHJ.

Dave

Re: GEC #89328
09/09/04 10:15 PM
09/09/04 10:15 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
GEC's are required to go from the electrode to the service equipment. If the disco at the meter is the service equipment, and it sounds like it is, this is code compliant.


Ryan Jackson,
Salt Lake City
Re: GEC #89329
09/09/04 11:21 PM
09/09/04 11:21 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
It can be anywhere from the load end of the drop to the disconnect enclosure.

250.24 Grounding Service-Supplied Alternating-Current Systems.
(A)(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.


Greg Fretwell
Re: GEC #89330
09/10/04 10:34 PM
09/10/04 10:34 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
What if all of the water piping in the house is PLASTIC? What do you ground to?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,514 Are you busy
180,311 Re: Forum
170,804 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9662 MB (Peak: 1.1049 MB) Zlib enabled. Server Time: 2018-01-17 01:16:27 UTC