More AFCI #89136
09/03/04 09:58 PM
09/03/04 09:58 PM
R
rknikko  Offline OP
Member
Joined: Feb 2004
Posts: 41
NY
I know that we cannot share the neutral or ungrounded wire for AFCI. Which mean no multi circuit wiring, otherwise we will need a 2 pole AFCI. BUT what about wiring the lights and receptacles under the same circuit? Will that cause the AFCI to trip? Will that cause the unbalance in neutral?

2017 / 2014 NEC & Related Books and Study Guides
Re: More AFCI #89137
09/03/04 10:33 PM
09/03/04 10:33 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I can't see where the unbalance would occur.

My worry has always been that every bedroom in a home would end up on one 20a AFCI. Using the 3va/sq.ft rule you could have 800 sq/ft of bedrooms on one circuit.


Greg Fretwell
Re: More AFCI #89138
09/04/04 07:20 PM
09/04/04 07:20 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
Quote
I can't see where the unbalance would occur.

My worry has always been that every bedroom in a home would end up on one 20a AFCI. Using the 3va/sq.ft rule you could have 800 sq/ft of bedrooms on one circuit.
The US NEC requires that the load be balanced so you have to evenly proportion the square footage over the Lighting and appliance branch circuits that are the result of the square footage computation. In other words if two thirds of the square footage is bedrooms then two thirds of the required L&A circuits must be used to serve them. If you install more L&A circuits than the code requires you still have to evenly proportion the square footage or the outlets over those circuits.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: More AFCI #89139
09/04/04 07:34 PM
09/04/04 07:34 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Tom I have heard that from other people and I have also heard that is not the case.

I really do not know the answer, where does the NEC spell this out?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: More AFCI #89140
09/04/04 08:54 PM
09/04/04 08:54 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
If someone is building to minimum code why would you expect the rest of the general lighting circuits to work out to much less than 3va per foot? 800 sq/ft is a lot of "bedroom" in a 1600 sq/ft house.


Greg Fretwell
Re: More AFCI #89141
09/04/04 09:23 PM
09/04/04 09:23 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Now isn't the 3va/sqft deal for calculation, not connection?

The circuit needs to be sized for what it is connected to....

Balance is not required, but strongly implied that some idea of balance on the connection is what they're looking for right?

Anyway, rknikko, I have had problems with AFCI's on certain types of loads. Dimmed LV lighting, flouresant lighting, and a flat screen monitor. If this type items have problems on a 2-wire circuit, why bother trying to chance it with a 3-wire?


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: More AFCI #89142
09/05/04 01:16 PM
09/05/04 01:16 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
I beleive 210-11(B) talks about this.

Re: More AFCI #89143
09/05/04 03:33 PM
09/05/04 03:33 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Yeah, was going to mention it, but started ww3 before on it....


Mark Heller
"Well - I oughta....." -Jackie Gleason

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,561 Are you busy
180,362 Re: Forum
170,840 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.056s Queries: 14 (0.039s) Memory: 0.9922 MB (Peak: 1.1523 MB) Zlib enabled. Server Time: 2018-01-20 10:59:02 UTC