BX in a MEDICAL Facility #89038
08/26/04 02:02 PM
08/26/04 02:02 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Is BX or MC cable allowed in a rural medical clinic with patient exam rooms and xray? wood structure single story

If I remeber correctly it is NOT.

thanks for any reply


Electricity has no respect for ignorance!
2017 / 2014 NEC & Related Books and Study Guides
Re: BX in a MEDICAL Facility #89039
08/26/04 04:52 PM
08/26/04 04:52 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
517-2 def. of a health care facilities.it includes a clinic. 517-13(a) lists MC as an acceptable wiring method, as long as it's outer metal sheath is identified as a grounding path. the MC cable has to have an insulated ground in it. It is usually called Hospital grade, and has a green paint on it.

[This message has been edited by trekkie76 (edited 08-26-2004).]

Re: BX in a MEDICAL Facility #89040
08/26/04 06:05 PM
08/26/04 06:05 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Very unlikely you will get MC with a sheath that is an acceptable grounding conductor, I use MC all the time and have never seen the type of MC that has the right kind of armor for grounding.

What you need is hospital grade AC cable.

The outer armor is a listed grounding conductor along with the added green grounding conductor.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: BX in a MEDICAL Facility #89041
08/27/04 06:23 AM
08/27/04 06:23 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Would there be any difference between hospital grade AC and hospital grade MC...other than the 'red hat' requirement [Linked Image]

-Jon

Re: BX in a MEDICAL Facility #89042
08/27/04 08:05 AM
08/27/04 08:05 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Jon, there is no such thing as HG MC.

Also remember that HCFC can not be used for Emergency Branch wiring.

Roger

Re: BX in a MEDICAL Facility #89043
08/27/04 09:47 AM
08/27/04 09:47 AM
C
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
Jon look at 250.118 (9) and 250.118 (11). That will explain the difference between AC & MC. Hospital grade Mc I'm told is custom order. Probably explains why I and iwire have not seen it.

Re: BX in a MEDICAL Facility #89044
08/27/04 11:26 AM
08/27/04 11:26 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Capt al, once again there is no such thing as hospital grade MC. There is MC with a sheath that is recognized as a ground per 250.118, and it is allowed for redundant grounding per 517.13, but that is not a Health Care Facility Cable.

Type HCFC is a true Armored Cable.

Go here for more info

Roger



[This message has been edited by Roger (edited 08-27-2004).]

Re: BX in a MEDICAL Facility #89045
08/27/04 03:39 PM
08/27/04 03:39 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
well then, someone should start making Hospital grade MC becuase it is listed as a wiring method in 517-13a. Just because you have never seen it doesn't mean it can't be used or doesn't exist.

Re: BX in a MEDICAL Facility #89046
08/27/04 05:33 PM
08/27/04 05:33 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Trekkie, did you check the link I posted?

As far as MC meeting the requirements of 517-13 (99 NEC reference) some types can meet this requirement and the smooth type is one of these, but this still is not a "Hospital Grade" cable.

Yes, I have seen the smooth type MC, and you have too most likely. Some appliances have it installed from the factory, but as Iwire says it is not common in our field.

And I will say again, Hospital Grade MC does not exist, HCFC is an AC hybrid. [Linked Image]

Roger

Re: BX in a MEDICAL Facility #89047
08/27/04 06:45 PM
08/27/04 06:45 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
the original post asked if mc was acceptable as a wiring method in a hospital. it is

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 15 (0.019s) Memory: 1.0229 MB (Peak: 1.2012 MB) Zlib enabled. Server Time: 2018-01-22 20:13:00 UTC