ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 10
Recent Posts
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Dimmable LED 2x4 lay in fixtures
by gfretwell. 04/22/17 01:14 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,483 Are you busy
169,112 Re: Forum
162,485 Need opinion
Who's Online Now
0 registered members (), 50 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#88966 - 08/19/04 08:18 PM Protecting NM cable with wood members  
jes  Offline
Member
Joined: Jul 2002
Posts: 103
CT
Two questions re. 300.4 and 550-15(C) (and similar)
First, for cables passing through wood members and without the required 1 1/4" setback: Has anyone experienced problems with sheathing fasteners (power driven staples or nails) missing the studs (and the protective plates for NM cable) and penetrating the cables?? As I read the NEC the plates DO NOT have to extend beyond the edges of the studs.

Second, 300.4(D) for cables PARALLEL to the studs and without the required 1 1/4" setback there appears to be an additional requirement for plate protection: If protection extending beyond the stud edge is required in this case where misdriven fasteners can impact the cable why not at drilled holes or notches?? What am I missing??


2017 / 2014 NEC & Related Books and Study Guides

#88967 - 08/19/04 08:47 PM Re: Protecting NM cable with wood members  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
You have missed nothing. The NEC has missed it. It seems as if someone needs to raise this omission with a code submittal.


Earl

#88968 - 08/20/04 04:48 AM Re: Protecting NM cable with wood members  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Jes If you are having problems with this happening to your cables go ahead and add additional protection nothing says you have to wait for the NEC. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#88969 - 08/20/04 07:39 AM Re: Protecting NM cable with wood members  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Hi Jes:

I was reminded of a proposal I sent in early in the 1990's.

I asked for the code to be changed to add 1/4" on each side of the "Kickplate" and CMP 3 said that was intended with the words I have bolded:

Quote
300.4(A)(1) Bored Holes.

...... Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by screws or nails by a steel plate or bushing, at least 1.6 mm ( in.) thick, and of appropriate length and width installed to cover the area of the wiring.


This is already included according to the panel, but now we have all new members and a new Chairman who may agree with replacing those vague and undefined words really not permitted by the style manual anyway.


Joe Tedesco, NEC Consultant

#88970 - 08/20/04 08:02 AM Re: Protecting NM cable with wood members  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
hear, hear


Earl

#88971 - 08/20/04 12:32 PM Re: Protecting NM cable with wood members  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
How do you all feel about the standoffs they use to hold Romex 1.25" to the side of a furring strip on a 3/4" furred masonry wall void?
The standard practice used to be to sleeve the Romex in EMT where it was unable to be 1.25" back. Now they are just using the plastic standoff to get a horizintal separation.
I can understand that the rocker will probably hit the furring +/- 1.25" but a homeowner hanging pictures might just keep poking holes until they hit something solid.


Greg Fretwell


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7757 MB (Peak: 0.9213 MB) Zlib enabled. Server Time: 2017-04-23 12:01:02 UTC