ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
AreMetal Ladders Ever OK For Electrical Work?
by gfretwell. 01/22/18 01:15 AM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 12 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Low voltage transformer??? Why??? #8867
04/07/02 10:34 PM
04/07/02 10:34 PM
M
Mike Wescoatt  Offline OP
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
Are there any advantages of using a 480-208/120 transformer versus a 7200 or 12470 volt primary transformer??? We're looking at a couple of 150KVA type K and about six 200KVA 208/120v standard xfmr's. Wouldn't the 12.47KV primary xfmr deal with load changes better than the 480V xfmr? Also, we would be able to cut down on supply amperage and physical size of the package with 12.47KV vs. 480v, right? Any thoughts??


Mike Wescoatt
Work Gear for Electricians and the Trades
Re: Low voltage transformer??? Why??? #8868
04/08/02 06:20 AM
04/08/02 06:20 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Are you wondering about the advantages of the utility supplying a high-tension (primary) service versus a 480 volt supply?

Re: Low voltage transformer??? Why??? #8869
04/08/02 08:27 AM
04/08/02 08:27 AM
S
smurf  Offline
Member
Joined: Mar 2002
Posts: 31
Benton, Ar. USA
Won't the utility co. supply your x-formers? If so, they determine what size according to your load needs. You can ask for a certain secondary voltage.

Re: Low voltage transformer??? Why??? #8870
04/08/02 09:03 AM
04/08/02 09:03 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Generally medium voltage (7kV or 13kV) service is better than low voltage (480V) for voltage drop, capacity and reduced conductor size.
You need to consider who will be servicing the transformer (on site personnel/electrician, a third party electrician or the utility.
Clearance and construction requirements help delineate installation differences.


Ron
Re: Low voltage transformer??? Why??? #8871
04/09/02 10:55 AM
04/09/02 10:55 AM
M
Mike Wescoatt  Offline OP
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
This will be in a refurb of a hotel showroom where the 480 is already existing. They keep on saying that they're strapped for supply already in this area. I was thinking we should pull a 12.47KV line to a distribution to deal with the 8-10 xfmrs we will need, but they want to keep the old 480V lines... Perhaps if it was 10,000A service...


Mike Wescoatt
Re: Low voltage transformer??? Why??? #8872
04/09/02 03:58 PM
04/09/02 03:58 PM
G
gpowellpec  Offline
Member
Joined: Dec 2000
Posts: 127
Irving, Tx USA
Who will supply and maintain the transformer? With deregualtion in Texas the customer would. Have you investigated the cost of going from a 480 voltage insulation rating to 12.47 kv? It seems the utility company would like to supply at the higher voltage (especially if the customer owns the transformer)because the losses on their side of the meter would be less.

Re: Low voltage transformer??? Why??? #8873
04/09/02 05:36 PM
04/09/02 05:36 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
How large an installation are you talking about (in additional load)?
There are big differences here.
You'd better be in the planning stages of this job?



[This message has been edited by electure (edited 04-09-2002).]

Re: Low voltage transformer??? Why??? #8874
04/11/02 08:49 PM
04/11/02 08:49 PM
M
Mike Wescoatt  Offline OP
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
All of the equipment will be customer owned and serviced by onsite Engineering department. We're still trying to come up with load sheets because we're in the early planning stages... We know the dimming system will need 208/120 700KVA service


Mike Wescoatt
Re: Low voltage transformer??? Why??? #8875
04/11/02 09:02 PM
04/11/02 09:02 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Is that a typo, or is the lighting dimming system need 2000 amps of capacity?


Ron
Re: Low voltage transformer??? Why??? #8876
04/11/02 10:45 PM
04/11/02 10:45 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Sounds to me that you are describing the typical "Customer Owned SDS" [Separately Derived System].

The Customer is supplied with a 480Y/277 VAC 3 Phase 4 wire system of -X- KVA [or MVA].

If the load calced was higher than what can be derived from a 480 VAC service, then this would have [or should have] been supplied by a 2400 VAC system, or a 4160 VAC system.

The Utility supplied Power System will be in respect to the Calculated Load. That's where the System Voltage becomes a factor.

Scott SET.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,592 Are you busy
180,388 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 1.0228 MB (Peak: 1.2011 MB) Zlib enabled. Server Time: 2018-01-22 14:07:10 UTC