#88454 - 06/04/04 09:13 PM Neutrals  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
Let's see if I can describe and ask this so that it makes sense to you all.

As I read the NEC 2002 Handbook, on a 208/120 3 phase circuit, coming from a 100 amp sub-panel with 12 breakers, it is proper (ok) to use one neutral for set:

Phase Breaker
A 1
B 3
C 5 these use one neutral

A 7
B 8
C 9 these use another neutral

A 11
B 13
C 15 these use a third neutral

Having said that, can I use the following set up?

Phase Breaker
A 1
B 3 this pair uses one neutral

C 5
A 7 this uses the second neutral

B 9
C 11 this uses the third neutral

A 13
B 15 this uses a fourth neutral

I hope this makes sense to you all.

Thanks

Steve


Thanks
Steve

2017 / 2014 NEC & Related Books and Study Guides

#88455 - 06/04/04 09:48 PM Re: Neutrals  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
What you listed should be fine but if these circuits are going to share one raceway you will need to adjust the ampacity of the conductors as shown in table 310.15(B)(2)(a). In your second example there are 12 current carrying conductors but if you did it the way shown in the first example there are only 9 current carrying conductors depending on the type of load.

Curt


Curt Swartz

#88456 - 06/05/04 06:42 PM Re: Neutrals  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
I see in the first example where you are using breakers 7-8-9 instead of 7-9-11. I hope this was a typo, and not reality.


Earl

#88457 - 06/07/04 12:23 PM Re: Neutrals  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
Yes, the first example should have said breakers 7,9,11 and then breakers 13,15,17.

Thanks for catching that.


Thanks
Steve


Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,138
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7596 MB (Peak: 0.8914 MB) Zlib enabled. Server Time: 2017-05-22 15:31:18 UTC