main bonding jumper #8838
04/06/02 04:30 PM
04/06/02 04:30 PM
D
dom  Offline OP
Junior Member
Joined: Jun 2001
Posts: 8
Can the manufacture supplied bonding strap in a normal 480v delta/120/208v wye transformer be used as the main bonding jumper for the separately derived system? Or must a properly sized bonding jumper be added according to the size of the secondary phase conductors?
Thanks

Work Gear for Electricians and the Trades
Re: main bonding jumper #8839
04/06/02 10:05 PM
04/06/02 10:05 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
The bonding strap that comes on most transformers is to bond the core frame not to act as a MBJ. You need to install a jumper sized by table 250-66 based on the secondary phase conductors from the equipment grounding lugs to the transformer XO.

Re: main bonding jumper #8840
04/07/02 11:27 AM
04/07/02 11:27 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Nick,
Doesn't the neutral also have to be connected to the Grounding Electrode System?
I have seen quite a few installations that only consisted of a jumper from XO to the transformer housing.
Please comment.

Re: main bonding jumper #8841
04/07/02 12:06 PM
04/07/02 12:06 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Redsy,
Yes. I always connect the neutral, GEC and bonding jumper at the XO terminal.

Where did they land the neutral?

Re: main bonding jumper #8842
04/07/02 02:29 PM
04/07/02 02:29 PM
D
dom  Offline OP
Junior Member
Joined: Jun 2001
Posts: 8
I always run my own MBJ from XO to a ground terminal in the xfmr. On smaller wires 1/0 and less I usually install a ground buss (having removed the paint under the buss) in the transformer to connect all the grounding conductors usually 5 or so.
1)MBJ from XO
2)grounding conductor to service equipment
3)grounding conductor routed with primary circuit to transformer
4)water bond conductor
5)GEC
On larger conductors is it ok to use several one or 2 port equipment grounding lugs for the purpose of tying all the grounding conductors together at one point?
Or is it necessary to obtain a ground buss, so the continuity of the grounding conductors isn't dependant on the transformer enclosure?
thank you

Re: main bonding jumper #8843
04/07/02 08:05 PM
04/07/02 08:05 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
It is not a code or listing standard that I know of but it is a good practice. I do that myself whenever possible.

Re: main bonding jumper #8844
04/08/02 06:17 AM
04/08/02 06:17 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Nick,

The neutral & GEC leave the xfmr enclosure, where they are bonded together, and go to the panelboard. The neutral connects to an insulated neutral bus. However the GC only connects to the panel enclosure. There is no connection to the Grounding Electrode System.
There are at least 3 setups like this at my site.

Dom,
If your GEC is run in your primary conduits, does that mean you have 2 in there? (1 as an EGC for the primary feeders and on 1 larger GEC for the secondary?)

Re: main bonding jumper #8845
04/08/02 05:59 PM
04/08/02 05:59 PM
D
dom  Offline OP
Junior Member
Joined: Jun 2001
Posts: 8
One EGC routed with the primaries based on the ocpd of the primary circuit.
The GEC connects directly to the ground electrode system in its own raceway, and/or just directly to the ground rod installed below the transformer through the concrete pad.

Re: main bonding jumper #8846
04/08/02 07:40 PM
04/08/02 07:40 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
dom,
Sorry, I misread your list. The reason I questioned it is because there was a previous thread discussing the GEC routed int the primary conduit.
Thanks.

Re: main bonding jumper #8847
04/08/02 09:38 PM
04/08/02 09:38 PM
D
dom  Offline OP
Junior Member
Joined: Jun 2001
Posts: 8
I've seen the primary equipment ground used as the GEC. I believe that is not permitted by NEC. That could form a long and indefinite path for a completed circuit from a lightning strike or overvoltage to the grounding system.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 14 (0.005s) Memory: 1.0064 MB (Peak: 1.1796 MB) Zlib enabled. Server Time: 2018-01-22 19:54:43 UTC