panel space #87913
05/01/04 10:22 AM
05/01/04 10:22 AM
V
velect  Offline OP
Member
Joined: May 2004
Posts: 81
st joseph mi usa
Almost every house I do that is over 3000 sq feet and has mostly electric appliances usually needs a sub panel. I think the NEC needs to approve a 200 amp 50 or 60 circuit panelboard for residential applications.

2017 / 2014 NEC & Related Books and Study Guides
Re: panel space #87914
05/01/04 11:29 AM
05/01/04 11:29 AM
T
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
One very important thing to keep in mind is that subpanels help reduce the length of branch circuits and thus reduce voltage drop. If you are installing the subpanel right next to the main panel in a new house then you are doing yourself and the customer a disservice. In new construction, subpanels should be placed on a different level and/or a different end of the home (relative to the main). Make sure one of the panels ends up close to the more heavily loaded areas like the kitchen. In an existing/fully-finished home, placing the sub next to the main may be your only reasonable choice.

I don't believe voltage drop is a real issue in many homes but a competent electrician still must take the issue into account. Having 200' long branch circuits in a home is something to be avoided!

Can you name even one case when you are going to use 50-60 circuit spaces feeding branch circuits in close proximity to the panel? If the loads are farther away then a subpanel is in order anyway.

Re: panel space #87915
05/01/04 11:33 AM
05/01/04 11:33 AM
T
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Have you done load calcs on the larger homes? Are you sure 200A is adequate?

Re: panel space #87916
05/01/04 11:49 AM
05/01/04 11:49 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I think triple has some good points on the voltage drop issue.

I will add that I am not in a hurry to see 60 circuits brought into one 14" W x 3" D enclosure.

If that was all two wire circuits that is 180 conductors, IMO it would be tough to keep neat.

If it is a case where 200 amps is enough power and you can locate the panels side by side get one panel Main breaker feed through style and get a second 200 amp main lug only panel.

Nipple them together with a couple of 2" nipples and for all intents and purposes you have 84 circuits in 'one' panel.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 21
Admin 19
Potseal 13
Popular Topics(Views)
243,514 Are you busy
180,311 Re: Forum
170,804 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.9582 MB (Peak: 1.0898 MB) Zlib enabled. Server Time: 2018-01-16 23:32:19 UTC