Article 408.15 #87841
04/22/04 03:38 PM
04/22/04 03:38 PM
D
Doug Scott  Offline OP
Member
Joined: Feb 2003
Posts: 24
Jonesville, Michigan, USA
I have a 30 circuit 100 amp MB panel. Have a total of 36 cicuits installed using 7 piggyback breakers. Was kicked down on inspection for overloading the panel. Panel does not state that piggyback breakers cannot be used.
Would this fall under Article 408.15 (2002)?
Doug

2017 / 2014 NEC & Related Books and Study Guides
Re: Article 408.15 #87842
04/22/04 03:55 PM
04/22/04 03:55 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
408.15 will not kick in until you get to 42 breakers (43 with your main)

Quote
Panel does not state that piggyback breakers cannot be used.


It shouldn't it has to tell you how many are allowed if any.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Article 408.15 #87843
04/22/04 04:09 PM
04/22/04 04:09 PM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
may i join in this one ??


ok i did look at the NEC 96 edition. old art. 384-15

" Number of overcurrent devices on one panelboard"
Not more than 42 overcurrent devices [other than those provided for in the mains] of a lighting and appliance branch-circuit panelboard shall be installed in any one cabient or cut out box.
A lightingand appliance branch-circuit shall be provided with physical means to prevent the installation of more over current devices than that number for which the panelboard was designged, rated, and approved.


so in my option here most imporat part that should read the breaker box label for listing for the numbers and types of breakers that approved for that usage

if i am off track let me know then i can correct my mistake here.

merci, marc

p.s. i did look at my french electrical codes and they say the same thing too.


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Article 408.15 #87844
04/22/04 07:38 PM
04/22/04 07:38 PM
S
Sparkeee32  Offline
Member
Joined: Mar 2004
Posts: 32
Federal Way WA USA
I would like to know the theoretical loads these circuits might have. For instance, are you running lots of 20 amp circuits, electric heaters, hot water heater, electric range.... or is everything gas, and you just have alot of lighting circuits? I have a feeling this is not about the # of breakers in the panel, but the size of all the conductors and the ampacities flowing through the said breakers. Some more specifics would be nice! Thanx! Brian!

Re: Article 408.15 #87845
04/22/04 07:49 PM
04/22/04 07:49 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Sparkeee24, you can have as many breakers as you want on a feeder, all that matters is the calculated load.

I have a 126 - 20 amp breakers on a 3 phase 225 amp triple tub panel at the job I am doing now, added up that would be 2520 amps. [Linked Image] In reality it is drawing a total of 150 amps (50 per phase)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Article 408.15 #87846
04/23/04 12:39 AM
04/23/04 12:39 AM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Doug, if possible please post the catalog number of the panel.

Curt


Curt Swartz
Re: Article 408.15 #87847
04/23/04 06:13 AM
04/23/04 06:13 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
I seem to recall somewhere a panel that was rated for a certain total rating of all of the breakers attached to it. I don't remember which, and I don't see why (if the calculated load and the feeder rating is less than the ampacity of the bars, who cares what the total of the CB ratings is), but if that is the listing, then that is the listing.

I have also seen panels where the instructions specifically limited the total rating of CBs connected to a single stab on the bus. This is more reasonable, since the rating of the stab might be less than that of the entire bus.

-Jon

Re: Article 408.15 #87848
04/23/04 04:04 PM
04/23/04 04:04 PM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
You are permitted to use all the spaces in a panelboard in accordance with its listing. If you have a 20/40 panelboard, you may use all the spaces and all of the circuit breakers may be ½" breakers. [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy
Re: Article 408.15 #87849
04/26/04 04:21 AM
04/26/04 04:21 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
This is a listing and labeling issue - 110.3(B). If the label lists this panel for a maximum of 30 ckts, that is all that is permitted. Reading the label will tell you if you are permitted to have more than 30 ckts (breakers).

Pierre


Pierre Belarge

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,508 Are you busy
180,291 Re: Forum
170,798 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 1.0013 MB (Peak: 1.1698 MB) Zlib enabled. Server Time: 2018-01-16 07:22:09 UTC