#87839 - 04/22/04 11:51 AM Fire Pumps  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Per 695.4 A a fire pump motor may be connected directly to the fire pump controller, bypassing any disconnect sw.(straigt from utility transformer) as long as the controller is a service rated listed controller,
Per 695.4 B a disconnect well be PERMITTED ,
but not required.
If a disconnect was installed it would be required to comply with 695.4 B (1)
Any comments ?? Hooking direct saves installing a Large disconnect sw(locked rotor current)
Wire size 125% full load current(695.6 c)


2017 / 2014 NEC & Related Books and Study Guides

#87840 - 04/24/04 08:18 AM Re: Fire Pumps  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
You have it correct already.

A disconnecting means or overcurrent protection is not required for the fire pump controller with the SUSE label since it already has the disconnecting means and overcurrent protection.

If you put in the overcurrent protection, it would have to carry locked current indefinitely. That would permit the fire pump motor to run to failure. Your overcurrent protection is only for short circuits and ground faults.

The controller will protect the wiring and the disconnect switch by interrupting the feed to the motor after 20 seconds of locked rotor current. At that point, the motor is already fried. That is why the switch and wire is sized the same as any other motor but the overcurrent protection is required to carry locked rotor current forever. [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy


Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7437 MB (Peak: 0.8628 MB) Zlib enabled. Server Time: 2017-07-22 20:53:17 UTC