14-2 switch leg on 20amp circuit #87639
03/31/04 08:53 PM
03/31/04 08:53 PM
R
Randy  Offline OP
Member
Joined: Sep 2002
Posts: 25
Concord, Va.
is it legal to use a 14-2 for a switch leg only on a 20 amp circuit?

2017 / 2014 NEC & Related Books and Study Guides
Re: 14-2 switch leg on 20amp circuit #87640
03/31/04 09:05 PM
03/31/04 09:05 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
NO!

It is an illegal branch circuit tap. Fixture wires are one of the few legal branch circuit taps. These are discussed in sections 402.10 and 402.11. You have a branch circuit, not fixture wires.


Ryan Jackson,
Salt Lake City
Re: 14-2 switch leg on 20amp circuit #87641
04/01/04 08:46 AM
04/01/04 08:46 AM
W
watthead  Offline
Member
Joined: Oct 2001
Posts: 172
South Carolina
What about a switch that controls a motor with thermal overload protection? [Linked Image]

Re: 14-2 switch leg on 20amp circuit #87642
04/01/04 09:25 AM
04/01/04 09:25 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Bob (Iwire) is right...this is a tough crowd! Watthead: I would agree with you on that one.


Ryan Jackson,
Salt Lake City
Re: 14-2 switch leg on 20amp circuit #87643
04/02/04 05:02 AM
04/02/04 05:02 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Yes the members here are on top of things.

That's good. [Linked Image] it forces me to look things up like I should be anyway [Linked Image]

Bob

I agree, no on the 14 AWG with the 20 amp lighting circuit.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 14-2 switch leg on 20amp circuit #87644
04/02/04 11:11 AM
04/02/04 11:11 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Reminds me of a thread a while back....some adamant discussions on a tap rule for #14 from #12 (20 amp circ OCP.

That thread had a lot of action....time permitting I'll have to look for it.

#14 switch leg off of a #12 20 amp, you get a red sticker!

As to Watthead's comment, yes thats allowable, but the original ?? seemed to lean toward a resi situation.

John


John
Re: 14-2 switch leg on 20amp circuit #87645
04/02/04 09:36 PM
04/02/04 09:36 PM
R
Randy  Offline OP
Member
Joined: Sep 2002
Posts: 25
Concord, Va.
when or is a #14 wire allowed on a 20 amp circuit ?

Re: 14-2 switch leg on 20amp circuit #87646
04/02/04 10:16 PM
04/02/04 10:16 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
Randy,

Circuits supplying motors and air conditioning equipment.

Case in point: The AC units at my house are ultra high efficiency.

Nameplate says:
Min circuit ampacity: 11 amps.
Min fuse/breaker: 15 amps
Max fuse/breaker: 30 amps

So the feed could be #14 protected by a 30 amp breaker.

Peter

[This message has been edited by CTwireman (edited 04-02-2004).]


Peter
Re: 14-2 switch leg on 20amp circuit #87647
04/04/04 05:17 PM
04/04/04 05:17 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
By Randy.
Quote
when or is a #14 wire allowed on a 20 amp circuit ?


14 AWG is rated 20 amps @ 60 C & 75 C, even 25 amps @ 90 C which helps when needing to derate.

The only thing that normally keeps 14 AWG on a 15 amp breaker is 240.4(D)

Quote
240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG, and 30 amperes for 10 AWG copper; or 15 amperes for 12 AWG and 25 amperes for 10 AWG aluminum and copper-clad aluminum after any correction factors for ambient temperature and number of conductors have been applied.


Notice the first part of that says:

"Unless specifically permitted in 240.4(E) through (G)"

(E) Tap Conductors.

(F) Transformer Secondary Conductors.

(G) Overcurrent Protection for Specific Conductor Applications

(G) has a table that lists about 10 applications that may allow 14 AWG on a breaker larger than 15 amps.

As Peter (CTwireman) pointed out HVAC equipment is one of those times, so are motors.

With the following nameplate data 14 AWG would be fine on a 30 amp breaker

Nameplate says:
Min circuit ampacity: 19 amps.
Max fuse/breaker: 30 amps

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,589 Are you busy
180,383 Re: Forum
170,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.003s) Memory: 1.0007 MB (Peak: 1.1650 MB) Zlib enabled. Server Time: 2018-01-22 06:23:23 UTC