#4 USE-2 #87524
03/15/04 12:27 PM
03/15/04 12:27 PM
R
REELECTRIC  Offline OP
Junior Member
Joined: Feb 2004
Posts: 5
Delafield, WI
I was given a reel of #4 USE-2 wire. It is also rated RHH and RWH I would like to use it up on 100 amp overhead residential service upgrades. Is there a resource (other than NEC 2002) for checking the ratings of a particular wire? Is any one familiar with this type?

2017 / 2014 NEC & Related Books and Study Guides
Re: #4 USE-2 #87525
03/15/04 02:37 PM
03/15/04 02:37 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Make sure your reel (or the wire) has a tag declaring it resistant to UV (sunlight).

Earl


Earl
Re: #4 USE-2 #87526
03/15/04 11:55 PM
03/15/04 11:55 PM
M
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
I am probably wrong about this, but I always thought that you need #2 use cable for 100amp service. I am assuming your reel is aluminum.

Re: #4 USE-2 #87527
03/16/04 09:17 AM
03/16/04 09:17 AM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Let me correct myself. Looking at the UL book for USE-2 (TYLZ) I see that USE and USE-2 are suitable for use where exposed to sun. But they are also NOT suitabe for use above ground, or in the premises, except to terminate at the service equipment or metering equipment. Default temerature rating is 75 degrees.
USE is designed to be used underground, but is allowed to be terminated aboveground at the service. I would venture to say it should NOT be used as a service riser.


Earl
Re: #4 USE-2 #87528
03/16/04 09:47 AM
03/16/04 09:47 AM
R
REELECTRIC  Offline OP
Junior Member
Joined: Feb 2004
Posts: 5
Delafield, WI
Thanks!

Re: #4 USE-2 #87529
03/16/04 11:20 AM
03/16/04 11:20 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Earl,
If the wire is dual rated as stated in the original post, then it can be used for the riser or anywhere else that RHW is permitted to be used.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9735 MB (Peak: 1.1195 MB) Zlib enabled. Server Time: 2018-01-22 20:09:44 UTC