ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
VFD MotorFeeders
by ghost307. 10/18/17 02:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,380 Are you busy
177,337 Re: Forum
168,952 Need opinion
Who's Online Now
0 registered members (), 54 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#87443 - 03/09/04 11:24 PM underground boxes & splices  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
314.28(C) says boxes need covers compatible with the box and suitable for the conditions of use, and 300.5(E) says direct-buried conductors or cables shall be permitted to be spliced or tapped without the use of splice boxes. The splices or taps shall be made in accordance with 110.14(B), "Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use."

So I go to troubleshoot a job last week and see sprinkler boxes enclosing weatherproof metal boxes, which should be ok to meet 314.29 for accessible boxes, but opening the j-boxes I see many boxes have an inch of water in them as the gaskets are not meant to be watertight, and some are open with mud in them. They used the blue wire-nuts with silicone sealant, but not done well, and some of the grounded conductors were nicked.

Sorry... so now for the question... am I missing a code section for boxes set on the ground in a sprinkler enclosure that would require sealed conduits entering these boxes, or that would not allow using the aluminum boxes we use for outdoor surface mounted work? The stainless steel covers and full 4-inch square black gaskets aren't going to keep moisture out. And 300.5(G) says conduits through which moisture may contact energized live parts shall be sealed or plugged at either or both ends... but if they used the sealed wire-nuts maybe that doesn't apply.

Sorry again... but 314.15(A) says in damp or wet locations boxes shall be placed or equipped so as to prevent moisture from entering or accumulating within the box and have to be be listed for use in wet locations. So if I put this kind of weatherproof but non-watertight box inside a sprinkler box on the ground, there is no way it will not collect water here in Oregon, so is that the answer? You can only use watertight boxes in the ground, or you may as well direct bury the wires and use the watertight splices? And those blue gel filled wire-nuts aren't meant to be used in underwater conditions are they?

Thanks... sorry it was so long.


2017 / 2014 NEC & Related Books and Study Guides

#87444 - 03/11/04 05:32 PM Re: underground boxes & splices  
watthead  Offline
Member
Joined: Oct 2001
Posts: 172
South Carolina
What voltage are we talking about?


#87445 - 03/11/04 07:39 PM Re: underground boxes & splices  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Are you saying you found "Bell" boxes in the ground? The only boxes I know of approved for UG are the "Quazite" type plastic or cement/fiberglass handholes. They do make splice devices approved for under water.

Earl


Earl

#87446 - 03/11/04 09:36 PM Re: underground boxes & splices  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
These are 125v circuits...

The splice kits I was talking about are like the 3M company makes, for instance... DBY-6 and DBR-6 UL Listed for 600V direct bury and submersion, UL File No. E102356... here's a data sheet... http://multimedia.mmm.com/mws/mediawebserver.dyn?yyyyyygeqJMySazyLazyyyb9X3tZeAqJ-

I think i posted some photos here once... can I still make avatars like 100kb and post them in a message? if that's ok, then I can include a few <100kb pictures of the boxes and splices


#87447 - 03/12/04 02:11 AM Re: underground boxes & splices  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Cindy;

Nice to see you again!
How's everything going?

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#87448 - 03/12/04 12:41 PM Re: underground boxes & splices  
watthead  Offline
Member
Joined: Oct 2001
Posts: 172
South Carolina
Cindy
You are on the right track with the DB kits from 3M. These are better than the gell filled wirenuts. I would prefer one of 3M's resin kits if the budget would allow, and it were available for the conductors (size and number) that you have. Good luck with the fix, and it sounds like they should have had you do the original installation.


#87449 - 03/15/04 11:20 PM Re: underground boxes & splices  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
hi scott35.. way busy, wish i had more time to visit and read things here.. you guys have a lot of good things to say... never enough time tho.. and like someone famous must have said, it seems like the more you learn, the more you are aware of that you dont know.
I'm not real critical of others who wired before me.. especially when i dont know the answers for sure, but this job wasnt done right.

anyway, i hope everyone here is still doing well, amking lots of money and enjoying whatever



Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 14 (0.003s) Memory: 0.7855 MB (Peak: 0.9391 MB) Zlib enabled. Server Time: 2017-10-19 03:44:25 UTC