ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/21/17 09:27 AM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,199 Are you busy
174,588 Re: Forum
167,022 Need opinion
Who's Online Now
0 registered members (), 51 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#87193 - 01/28/04 11:18 PM Code and Data Networks  
jgwiii  Offline
Junior Member
Joined: Jan 2004
Posts: 1
Blanchard, Oklahoma, USA
Hello,

I'm a small contractor and I'm currently installing a data network in a new school building. I was told to place the data rack containing two cisco switches and a punch down in a utility room that has a water heater and an electrical panel in it. Sunsequently, two other contractors bidding on jobs at the school remarked that to have this 4U open rack in that room with the water heater and electrical panel is a violation of code. I have done similar installations in this same county and state (oklahoma) in utility rooms with both water heaters and electrical panels and the installations have passed final fire code and building inspections and so forth. The room its self is approximately 4X8. Is there a basis for concern that has been over looked in the past regarding this? Thanks for any help on this matter.


2017 / 2014 NEC & Related Books and Study Guides

#87194 - 01/29/04 10:23 AM Re: Code and Data Networks  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It's not the water heater that may be a problem. It is the fact that many times the space in front of the electrical panel is taken by "other" trades. There must be a working space clearance in front of all electrical panels 3 to 3-1/2 feet deep (depending on voltages), and as wide as the panel, but no narrower than 30 inches.
There is also a "dedicated equipment space" to avoid. The dedicated space extends from the floor to 6 feet above the panel, or to the structural ceiling, if lower, and is equal to the depth and width of the panel. Nothing above or below the panel is allowed except electrical installation stuff.
Keep out of these areas, and you are OK.

Earl


Earl


Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,853
Joined: April 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7439 MB (Peak: 0.8609 MB) Zlib enabled. Server Time: 2017-07-22 06:53:16 UTC