lighting load on nuetral #87187
01/28/04 09:18 PM
01/28/04 09:18 PM
B
barbwire  Offline OP
Junior Member
Joined: May 2003
Posts: 17
There's been many times in the past where I have seen 4 wire homeruns carrying 3 277 volt lighting circuits,in some situations all three circuits contain a large amount of lights in each. Is this a code violation, just bad practice or acceptable?

2017 / 2014 NEC & Related Books and Study Guides
Re: lighting load on nuetral #87188
01/28/04 09:48 PM
01/28/04 09:48 PM
A
abode electric  Offline
Junior Member
Joined: Jan 2003
Posts: 8
I don't think its a violation. It can be a bad way to wire fluorescent lighting. The neutral load can become unbalanced due to harmonics.

Re: lighting load on nuetral #87189
01/28/04 11:31 PM
01/28/04 11:31 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I have heard that many people consider the nuetral of the circuit you describe as current carrying, due to the non-linear loads of flourescant lights. You might ask your electrical engineer if 310.15(4) applies. The thing to remember, however, is that at 90 degrees a #12 conductor is good for 30 amps, but only for the purposes of derating. Since you are describing a situation that may be 4 current carrying conductors in a raceway, you are permitted to use 30amp rating to derate...80% of which is 24 amps. Since 240.4(D) requires that a #12 conductor be supplied from a breaker not larger than 20 amps, it really is a moot point until you have 10 current carrying conductors in a raceway.

Hope this helps [Linked Image]


Ryan Jackson,
Salt Lake City
Re: lighting load on nuetral #87190
01/29/04 09:58 AM
01/29/04 09:58 AM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The modern electronic ballast has solved the problem of harmonics. Buy the expensive kind, or run #8 white wire for the neutral home runs (super-neutral) like they do for cubicles.
But, we have run the 4-wire home run, or even the 8-wire home run for years with no ill effects. (until harmonics)


Earl
Re: lighting load on nuetral #87191
01/29/04 01:22 PM
01/29/04 01:22 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Earl,
Quote
The modern electronic ballast has solved the problem of harmonics.

I thought that the electronic ballasts cause even more harmonics than the magnetic ballasts. That being said, I've never seen a problem with a neutral caused by harmonics on a multiwire lighting circuit.
Don


Don(resqcapt19)
Re: lighting load on nuetral #87192
01/30/04 08:03 AM
01/30/04 08:03 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
As mentioned, the Common Grounded Conductor on a 3Ø 4W Wye system will carry at least the same level of Current of that found on the Ungrounded Conductor with the highest Load Current - for L-C connected Loads.

Under some circumstances, the Common Noodle will carry little to no Load Current (for L-C loads). These are very specific in nature, and mostly apply to Pure Resistance Loads.

For most applications, figure the Common Noodle to carry at least what the largest Load Current of any ØA, ØB or ØC line is.
Example:

Multiwire (4 Wire) circuit, 20 amp rating, reactive loads (no load is pure resistance only), THD is <1% overall:

ØA Load = 8 Amps,
ØB Load = 10 Amps,
ØC Load = 12 Amps.
Common Grounded Conductor will carry ± 12.3 Amps.

Another example:
If Loads with THD of 33% overall are connected to the same systems + Multiwire Circuitry, and:
ØA Load = 10 Amps,
ØB Load = 10 Amps,
ØC Load = 10 Amps.
Common Grounded Conductor will carry ± 20 Amps.

Harmonics are produced by many types of loads besides Fluorescent Lamp Ballasts. SMPS for Computers, AC Induction Motors, Linear Power Supplies, UPS Equipment, AC Coils for Relays and Contactors, Dimmers, and even TVSS devices are generators of Harmonics.
Magnetic (Reactor-Core type) Ballasts generate Harmonics, as well as Hybrids and straight Electronic Ballasts - for both Fluorescent and HID Lighting.

Multiwire Circuitry is Code Compliant, and if done properly, can be beneficial.
Installation requires knowledge of load types, and for the best installations / designs, those factors should be applied to determine maximum loads + conductor sizing.

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9770 MB (Peak: 1.1236 MB) Zlib enabled. Server Time: 2018-01-20 01:03:31 UTC