#87182 - 01/28/04 08:05 PM Places of Assembly 518-4  
dshipcott  Offline
Junior Member
Joined: Jul 2003
Posts: 5
Los Angeles, CA
518-4 says that non metalic raceways shall be encased in 2" of concrete. Other than under a concrete slab, can you give an example of an installation that would include a 2" concrete envelope around the conduit?
Is the code refering to non metalic conduit runs outside of the building that feed or support places of assembly?


2017 / 2014 NEC & Related Books and Study Guides

#87183 - 01/28/04 09:56 PM Re: Places of Assembly 518-4  
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
Encased would mean surrounded by concrete.

I had to change a word from conduit to concrete.

[This message has been edited by russ m (edited 01-28-2004).]


#87184 - 01/28/04 10:02 PM Re: Places of Assembly 518-4  
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
The code is saying if you use non metalic raceway it has to be surounded by concrete, unless it is allowed in (B) or (C)


#87185 - 01/28/04 11:54 PM Re: Places of Assembly 518-4  
dshipcott  Offline
Junior Member
Joined: Jul 2003
Posts: 5
Los Angeles, CA
Thanks for your replys.
So in the exception you can install PVC in a conferance and meeting room but not a Multipurpose room because a multipurpose room is an area listed as a place of assembly not included in the exception.
What does not make sense about that interpretation is that many of the rooms not listed in the exception are interchangeable with the rooms listed in the exception.


#87186 - 01/28/04 11:59 PM Re: Places of Assembly 518-4  
dshipcott  Offline
Junior Member
Joined: Jul 2003
Posts: 5
Los Angeles, CA
Here is the origin of my interest in this subject. A structural engineer stated that a 3/4" PVC conduit installed in a structural concrete deck had to be spaced 2” from the face of the finished concrete. He sighted NEC 518-4 as the reason for the requirement. The structural deck is in between a parking level below and meeting rooms above.



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7672 MB (Peak: 0.9062 MB) Zlib enabled. Server Time: 2017-10-19 07:17:15 UTC