4 - 1/0 IN 2inch LB #87075
01/16/04 07:59 PM
01/16/04 07:59 PM
L
LK  Offline OP
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Can you put 4 - 1/0 in a 2" LB ?

2017 / 2014 NEC & Related Books and Study Guides
Re: 4 - 1/0 IN 2inch LB #87076
01/16/04 08:54 PM
01/16/04 08:54 PM
G
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
Look in the inside of the LB for max wire size and number

Re: 4 - 1/0 IN 2inch LB #87077
01/16/04 10:01 PM
01/16/04 10:01 PM
L
LK  Offline OP
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Max wire size is 4/0 as in all 2" LB's however max fill notes not more than 3 conductors, it seams for conductors over #4 three is the limit, fittings are not the same fill as conduit. This would prevent using 2" LB for 3PH Service LB.

[This message has been edited by LK (edited 01-16-2004).]

Re: 4 - 1/0 IN 2inch LB #87078
01/17/04 07:55 PM
01/17/04 07:55 PM
R
rizer  Offline
Member
Joined: Jan 2004
Posts: 91
bradenton ,fl.,usa
you could always use a larger lb with reducing ends.

Re: 4 - 1/0 IN 2inch LB #87079
01/17/04 08:46 PM
01/17/04 08:46 PM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
314.28 Pull and Junction Boxes and Conduit bodies.(A)(2) would require more than a standard LB. It usually requires a mogul LB.

Re: 4 - 1/0 IN 2inch LB #87080
01/17/04 09:00 PM
01/17/04 09:00 PM
L
LK  Offline OP
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Russ,
You got it, I posted for one of my guys, He said there is nothing wrong with using a regular LB, he din't get a mogul because the supply house din't stock them, and if they had to order, it would cost more. I stopped the job and refuse to let them use the regular LB. Their answer is, we see everyone else use them, and is the inspector going to ask you to tear down the job. I don't want to take that chance.
Rizer,
The larger LB with a reducer will not meet the requirements of 314.28(A)(1), it is still to short in length. Only the Mogul LB will do it.

[This message has been edited by LK (edited 01-17-2004).]

Re: 4 - 1/0 IN 2inch LB #87081
01/18/04 10:53 AM
01/18/04 10:53 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
LK,
Max 4/0, as with all 2" LBs?
I think you'd be better off to follow gserve's instruction, and look in the inside of the LB.
From the OZ/Gedney catalog:
LB-200A = Max 3 #4/0 AWG, (aluminum for rigid)
LB-67 = Max 3 #1/0 AWG, (a Form 7 LB)

I regularly see the use of 2" Appleton LB's (aluminum) Max 2/0 with 3/0 wire on 200 Amp circuits...S

[This message has been edited by electure (edited 01-18-2004).]

Re: 4 - 1/0 IN 2inch LB #87082
01/18/04 01:18 PM
01/18/04 01:18 PM
L
LK  Offline OP
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Electure,
Max 4/0, as with all 2" LBs? is the comment from one of my guys, that asked me to post this, He had a carlon LB 2" J type that has 4/0 stamped inside. He now knows that all LB's are not equal. style and type for different applications. They forget bending space and fill requirements when it comes to LB's. Yes you will see this violation many times.


[This message has been edited by LK (edited 01-18-2004).]

Re: 4 - 1/0 IN 2inch LB #87083
01/18/04 04:41 PM
01/18/04 04:41 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
Sorry and no offense, LK
I guess I didn't quite understand.
Another way to accomplish this (LB) in certain circumstances is to use a section of wireway with the required distance between conduit entry points. They're sure a lot less expensive, and more easily available than the mogul conduit bodies...S



[This message has been edited by electure (edited 01-18-2004).]

Re: 4 - 1/0 IN 2inch LB #87084
01/18/04 09:13 PM
01/18/04 09:13 PM
L
LK  Offline OP
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
electure,
We are doing a 200A 3 phase system next week, and I am using a box on the inside of the building, basement area, if I can find one with the proper gauge for service conductors. Still using mogul outside, you can guess what a 2-1/2" mogul LB costs. By the way, one of the guys called today and said he wanted to thank me for giving him the chance to be an electrician.

[This message has been edited by LK (edited 01-18-2004).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,558 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.003s) Memory: 1.0074 MB (Peak: 1.1835 MB) Zlib enabled. Server Time: 2018-01-20 03:25:13 UTC