Solid or Stranded #86976
12/27/03 03:56 PM
12/27/03 03:56 PM
R
Ryan_J  Offline OP
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I have long heard the argument about solid or stranded #8 bonding jumpers being used to satisfy 680.74

I ran into this the other day:
[Linked Image]

[Linked Image]

This is a 1/0 for a hydromassage tub!!! The installer was upset with me for requiring a 1/0 to bond his service lateral conduit, so he decided to bond everything with 1/0.

[This message has been edited by Ryan_J (edited 12-27-2003).]


Ryan Jackson,
Salt Lake City
2017 / 2014 NEC & Related Books and Study Guides
Re: Solid or Stranded #86977
12/27/03 11:19 PM
12/27/03 11:19 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[quote]requiring a 1/0 to bond his service lateral conduit ..[/quote}

Ryan:

Please explain the scenario?


Joe Tedesco, NEC Consultant
Re: Solid or Stranded #86978
12/28/03 07:58 PM
12/28/03 07:58 PM
R
Ryan_J  Offline OP
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Joe: The service entrance conductors are rated for 400 amps. 250.102 (C) refers one to 250.66 for bonding jumpers installed on the line side of the service disonnecting means.

Very popular residentail installation in my neck of the woods.


Ryan Jackson,
Salt Lake City
Re: Solid or Stranded #86979
12/28/03 08:34 PM
12/28/03 08:34 PM
R
Ryan_J  Offline OP
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
THREADJACK!!!

We had a very nice discussion about bonding the line side of a service at this thread:

http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=7;t=000426


Ryan Jackson,
Salt Lake City
Re: Solid or Stranded #86980
07/29/04 10:08 PM
07/29/04 10:08 PM
S
stamcon  Offline
Member
Joined: Mar 2001
Posts: 330
So San Francisco CA
So, what's the answer to stranded or solid? With the wording "not smaller than a No. 8 solid", is the code describing the actual diameter of the conductor, with a stranded being larger than a solid of the same gage?


Steve
Re: Solid or Stranded #86981
07/29/04 10:44 PM
07/29/04 10:44 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
I read that as 8 Ga solid or a larger stranded size. The only place I know of that allows stranded 8ga for pool bonding is the bond wire in the PVC raceway to a wet niche forming shell. You can use stranded for equipment grounding (not the same thing).


Greg Fretwell
Re: Solid or Stranded #86982
07/30/04 08:28 AM
07/30/04 08:28 AM
R
Ryan_J  Offline OP
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
As written, I beleive you could use #8 stranded, but I'm not sure that that is the intent.

Compare the language of 680.74 to that of 680.26


Ryan Jackson,
Salt Lake City
Re: Solid or Stranded #86983
07/30/04 10:13 AM
07/30/04 10:13 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
I agree 680.26(C) does say "solid copper conductor". I also see that they call the 8ga in the PVC to the forming shell an EGC, not a bond 680.23(B)(2)(b)
I guess there is method to the madness.


Greg Fretwell
Re: Solid or Stranded #86984
07/31/04 10:56 AM
07/31/04 10:56 AM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
Ryan
What size conductor did the installer wish to bond the service conduit (or conduits??)with??


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,596 Are you busy
180,394 Re: Forum
170,865 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.005s) Memory: 0.9995 MB (Peak: 1.1666 MB) Zlib enabled. Server Time: 2018-01-23 02:24:24 UTC