Grounding electrode conductor #86596
11/14/03 12:23 PM
11/14/03 12:23 PM
E
electrician02125  Offline OP
Member
Joined: Feb 2001
Posts: 89
Good afternoon

I am wiring a residential building with 4 units. Each of the units will have their own water supply and meter. I have installed the typical 5 gang meter pack (4 plus public)with service disconnects directly next to the meters.

For grounding I have ran a continuous number 2 copper conductor the length of the building and split bolt connected short lengths down to each water line to bond all back to the main service equipment ground lug. I have also driven a supplemental ground rod at the meter enclosure and ran number 4 to the rod as a supplemantal ground.

The Inspector loved it but I would like your opinion.

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding electrode conductor #86597
11/14/03 10:16 PM
11/14/03 10:16 PM
E
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
I thought the code did not allow reversable connections on the grounding system or the GEC or the water pipe bond.

Edward


Thanks
Edward
Re: Grounding electrode conductor #86598
11/15/03 07:10 AM
11/15/03 07:10 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
If you ran the gec continuous to one electrode then tapped off using split bolts to each unit water service you are not splicing the electrode. The taps are really bonding jumpers to each addtional water service. You should have two supplemental rods unless you have 25 ohms or less on one. You only need # 6 to the rods.

Re: Grounding electrode conductor #86599
11/15/03 07:21 AM
11/15/03 07:21 AM
B
Branch  Offline
Member
Joined: Apr 2003
Posts: 13
West Alexandria, Ohio, Preble
You might want to look at Art: 250.64(C)this will explain the type of splice connectors allowed for grounding. (Irreversible compression-type connector) (Exothermic welding process)

Re: Grounding electrode conductor #86600
11/15/03 08:03 AM
11/15/03 08:03 AM
B
Branch  Offline
Member
Joined: Apr 2003
Posts: 13
West Alexandria, Ohio, Preble
I think if you have water service in each unit that will be a main ground you have to run seperate grounds from each water line back to your service equipment.

Re: Grounding electrode conductor #86601
11/15/03 08:40 PM
11/15/03 08:40 PM
R
RickG  Offline
Member
Joined: Jul 2001
Posts: 37
South County, R.I. USA
From what I gathered from the info provided, the water pipes in each unit are bonded, they are not ground electrodes. I am assuming that the underground portion of the water services is plastic, if not the following does not apply. The code requires a continuous conductor to the main ground electrode, in this case the ground rods. The H2O bond wire is allowed to be tapped/spliced as long as it is sized to the service entrance conductors, not the breaker size. I don't know what size SE conductors were run, but fromwhat I see this is a code compliant installation.
Now after rereading the original post, if the water underground services are indeed metalic... you would have to go to the main ground electrode unspliced. Could any ONE of the water services be the main ground electrode and the other 3 be supplental?
I think that is how I would look at it in my town.
If this is the case as long as you go to any one of the water services unspliced (even the last one) you could splice to the other 3.

Re: Grounding electrode conductor #86602
11/16/03 06:17 AM
11/16/03 06:17 AM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
If the water service is metal underground it sounds code compliant to me.

Re: Grounding electrode conductor #86603
11/16/03 07:28 AM
11/16/03 07:28 AM
B
Branch  Offline
Member
Joined: Apr 2003
Posts: 13
West Alexandria, Ohio, Preble
If the main water services are plastic entering the building i think you can run your bond back to each sub-panel in each unit or you can splice the bonds and run back to service equipment or to ground rod or rods. Any thoughts on this would be a help to understanding this.

Re: Grounding electrode conductor #86604
11/16/03 08:40 AM
11/16/03 08:40 AM
E
electrician02125  Offline OP
Member
Joined: Feb 2001
Posts: 89
Thank you all for the input.

The 3 water services are all copper throughout. I do in fact have a continuous connection from the furthest water service back to the main GEC lug. The remaining two water services I have simply exposed some of the copper on the continuous GEC and split bolted them that way. Sort of like a continuous ground bus running the length of the building. On one end I have the conductor landed on the main GEC lug and the other is on the furthest water line....continuous with no breaks in the conductor. I hope this makes sense.

Re: Grounding electrode conductor #86605
11/16/03 07:41 PM
11/16/03 07:41 PM
R
RickG  Offline
Member
Joined: Jul 2001
Posts: 37
South County, R.I. USA
02125
Sounds like a fine, code compliant installation to me.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,592 Are you busy
180,388 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 1.0080 MB (Peak: 1.1818 MB) Zlib enabled. Server Time: 2018-01-22 12:10:42 UTC