#14 taps on 20 amp circuit #86213
09/25/03 09:04 PM
09/25/03 09:04 PM
C
CTwireman  Offline OP
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
I had an interesting discussion today. I was told by an electrical contractor that they used #14 pigtails for all their receptacle connections on 20 amp ciruits.

Their justification for this pratice is that they install 15 amp receptacles, and that the circuit should never be loaded above 16 amps anyway.

They say that they pass inspection, and I believe that since these jobs are not hidden from the public eye. They are in big-name retail stores in major malls in this area.

I took the liberty of calling them "hacks" and of course I was scoffed at. [Linked Image]


Peter
2017 / 2014 NEC & Related Books and Study Guides
Re: #14 taps on 20 amp circuit #86214
09/26/03 05:10 AM
09/26/03 05:10 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
From Mike Holts newsletter.
Q8. I have an issue where a contractor used 15A, 125V receptacles on a 20A circuit with 12 AWG conductors. In addition, the contractor used 14 AWG tap conductors to the 15A receptacles. I feel that a 20A rated receptacle is required and the conductors to the receptacle shall be a minimum 12 AWG. Am I right?

A8. Almost. A 15A rated receptacle can be connected to a 20A branch circuit that supplies two or more receptacles (this would include a single duplex receptacle, because it contains two receptacles) [210.21(B)(3)]. However, the tap rule contained in 210.19(A)(4) Ex. 1(c) clearly states that branch circuit taps are not permitted for receptacles. So the 15A receptacles are fine, as long as there are at least two of them on a circuit, but the 14 AWG pigtails are a Code violation

Re: #14 taps on 20 amp circuit #86215
09/26/03 07:31 AM
09/26/03 07:31 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Probably confusion with the allowable taps for 'outlets' in Exception 1 of 210.19.(4) and also shown in table 210.24. If I understand this correctly, in a 20A (or even a 30A) circuit, you are allowed to have 14ga tap wires to an 'outlet'...but the outlet must _not_ be a receptacle outlet.

This makes sense since many outlets are fixed known loads, but receptacle outlets have the capability of being loaded until the breaker trips.

-Jon

Re: #14 taps on 20 amp circuit #86216
09/26/03 12:36 PM
09/26/03 12:36 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It’s hard to imagine there could be more than a few pennies saved for a foot of #12, possibly larger splices and extra labor needed. Maybe for single receptacles at best, but certainly not duplex...

Re: #14 taps on 20 amp circuit #86217
09/26/03 02:03 PM
09/26/03 02:03 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Bjarney, I would think the extra effort to carry #14 wire around for these pigtails would cost more.

I think there is probably a sinister reason behind this practice, they are using backstab devices.

Of course it may just be the installers have weak hands. [Linked Image]

Roger

Re: #14 taps on 20 amp circuit #86218
09/26/03 02:33 PM
09/26/03 02:33 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Before the rocks start flying.....
Most installations are inspected "rough" and "final". On "rough", most times, the "tails" are not made-up, unless it's a multi-wire circuit, then the neutrals are tailed. At "final", all the devices, plates, etc, are installed, and the AHJ doesn't take anything "apart" device wise.

Personally, a comm EC that uses #14 tails is not the "norn" around here, as I have never heard of this. (As an EC and an AHJ). Not saying someone would "do it", but it's very doubtful.

The 32 sq mile twp that I am an AHJ in has "everything" from a major regional mall, to office complexes, strip malls, retail, warehouses, hospital, chem plants, and tons of resi, and I have not come across this.

As Bjarney implied, doubtful if it's a $$$ move.

John


John
Re: #14 taps on 20 amp circuit #86219
09/26/03 05:23 PM
09/26/03 05:23 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
John, our local inspectors will have random receptacles and switches opened up in their finals. If we are in a state final it isn't uncommon for 50% of all devices to be opened.

In both of the above it does depend on whether you are new to the inspectors and your past history with the them.

Roger

Re: #14 taps on 20 amp circuit #86220
09/27/03 07:46 AM
09/27/03 07:46 AM
G
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
Several years ago, had a new contractor.

He had several one and two family dwellings to wire and he used EMT.

I bet he lost money on the first unit.

He used 12AWG and 20A CB's.

When he got to the first junction box he changed to 14 AWG.

Was that $$$$ ?

Re: #14 taps on 20 amp circuit #86221
09/27/03 01:03 PM
09/27/03 01:03 PM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
I've seen this more recently in residential work...EC's using #12 NM and those cheap duplex from Home Depot....you used to be able to backstab these with the #12, now you need a #14...so they pigtail with #14.

Re: #14 taps on 20 amp circuit #86222
09/27/03 09:53 PM
09/27/03 09:53 PM
T
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
EXCELLENT answer Electricmanscott! It is nice to see others referencing known/reliable sources (other than the often ambiguous code-book). Forums would be quite desolate without opinions. However, opinions alone have their limits and are all too often misconstrued as facts.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,510 Are you busy
180,296 Re: Forum
170,800 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.003s) Memory: 1.0245 MB (Peak: 1.2000 MB) Zlib enabled. Server Time: 2018-01-16 13:10:26 UTC