#86085 - 09/06/03 10:09 PM Max distance between underground service and inside disco?  
Chris Rudolph  Offline
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
Here is the situation,
Residential customer wants to locate his meter socket 50ft from his new house and run the service conductors(4/0 3cond URD) 18in under grade in conduit(for the 50ft) through the foundation wall into a 4ft high crawl space and then another 8ft to the floor of the utility room and then up to the disco/load center combo.I believe the code says that the inside disco shall be located nearest the point of entrance of the service conductors.Is 8ft close enough?
Chris


2017 / 2014 NEC & Related Books and Study Guides

#86086 - 09/07/03 08:29 AM Re: Max distance between underground service and inside disco?  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
"Nearest" is a judgement call by the AHJ. I would have a hard time accepting 8 feet, especially since it is concealed from view.

I'd vote for an outside disconnect.

Tom


Few things are harder to put up with than the annoyance of a good example.

#86087 - 09/07/03 09:06 AM Re: Max distance between underground service and inside disco?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
In this area the "magic number" seems to be 5' inside the building.

If the customer insists on this you can encase the raceway in 2" of concrete and be "outside" the building as far as you want inside the building.

Quote
230.6 Conductors Considered Outside the Building.

Conductors shall be considered outside of a building or other structure under any of the following conditions:

(1)Where installed under not less than 50 mm (2 in.) of concrete beneath a building or other structure

(2)Where installed within a building or other structure in a raceway that is encased in concrete or brick not less than 50 mm (2 in.) thick


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#86088 - 09/07/03 10:09 AM Re: Max distance between underground service and inside disco?  
sparky806  Offline
Member
Joined: Dec 2002
Posts: 59
Shawnee, KS, USA
Why dont you just put the disco 0n the pole with the meter, and run 4 conductors to the house panel?


#86089 - 09/07/03 01:52 PM Re: Max distance between underground service and inside disco?  
Chris Rudolph  Offline
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
Good suggestions guys!The customer doesn't want any "electrical clutter"on the side of the new house.I think I will have the AHJ come out and take a look see,before I run any service.All the other rough in is complete.
I thought that I had this all agreed to before I started this rough in but the customer changed his mind however he is willing to pay the extra.OK with me!
Chris


#86090 - 09/08/03 06:13 PM Re: Max distance between underground service and inside disco?  
Chris Rudolph  Offline
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
The AHJ voted to put the meter AND a disco on a pedestal across the driveway and run 4 wire into conduit into the house.He has my vote.
He also signed off on the rough in.Wonders never cease!!
Chris


#86091 - 09/09/03 06:54 AM Re: Max distance between underground service and inside disco?  
RickG  Offline
Member
Joined: Jul 2001
Posts: 37
South County, R.I. USA
Remember to establish a ground electrode system at the house, even if you set electrodes at the pedestal. Code requires a electrode system at each structure served. Code wise, I don't think that a ground electrode system is required at the pedestal, as the pedestal would not be considered a structure. If it were my job, I would set an electrode at the pedestal in addition to the required electrode system at the house.
Rick


#86092 - 09/09/03 03:07 PM Re: Max distance between underground service and inside disco?  
rmiell  Offline
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
"Why dont you just put the disco 0n the pole with the meter, and run 4 conductors to the house panel?"

What does this have to do with the question? You are required by code, to follow the same rules whether it is a service or a feeder. see Article 230.70(A) and 225.32.

Rick Miell


#86093 - 09/09/03 03:22 PM Re: Max distance between underground service and inside disco?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Strange how 230.70(A) says

Quote
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.


So it seems outside could be any readily accessible location.

But 225.32 says

Quote
The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors.


So for 225.32 even an outside disconnect has to be nearest the point of entrance.

Bob



[This message has been edited by iwire (edited 09-09-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#86094 - 09/09/03 10:10 PM Re: Max distance between underground service and inside disco?  
Chris Rudolph  Offline
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
Based on the code info presented I am ready to put the meter socket and the disco within 5 feet of the outside the house on a pedestal with the double set of electrodes(one for the pedestal and one for the inside panel).Thank you for your help.
Chris



Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.023s Queries: 14 (0.004s) Memory: 0.8103 MB (Peak: 0.9872 MB) Zlib enabled. Server Time: 2017-07-20 22:35:16 UTC