#85997 - 08/27/03 06:21 AM code question  
skidmark  Offline
Junior Member
Joined: Aug 2003
Posts: 2
clarkesville, ga. U.S.A
I saw a resedential panel in which the electrician had pulled all of the circuits thru a piece of 2 inch pvc conduit. Isn't this a code violation and if so where is it in the 2002 N.E.C.?


2017 / 2014 NEC & Related Books and Study Guides

#85998 - 08/27/03 07:05 AM Re: code question  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Unless there was damage to the conductors, I don't think it's a violation. Why do you?


Ron

#85999 - 08/27/03 07:12 AM Re: code question  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Although there are exceptions, this practice would be a violation of the basic rule of 312.5(C).
However, this tpye of installation does seem to be common in some areas of the country.


#86000 - 08/27/03 09:46 AM Re: code question  
GEO  Offline
Member
Joined: Mar 2003
Posts: 47
Lancaster,Pa
as stated there are exceptions.
this is allowed provided you meet those conditions.


#86001 - 08/27/03 09:49 AM Re: code question  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Unless there were very few cables involved, I don't see how this installation could be in compliance with the previously mentioned 312.5(C). I've measured a few brands of Romex & depending on the wire gauge, the limit could be as few as 5 cables in a 2" PVC. Also, very often the requirement for derating is overlooked in this type of installation.

Tom


Few things are harder to put up with than the annoyance of a good example.

#86002 - 08/27/03 06:43 PM Re: code question  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Fill derating does not apply if it the conduit is installed for protection from physical damage only and is not a complete conduit system.
See Chapter 9, Table 1, Note 2


Ron

#86003 - 08/27/03 09:18 PM Re: code question  
skidmark  Offline
Junior Member
Joined: Aug 2003
Posts: 2
clarkesville, ga. U.S.A
According to 312.5(c) it is a code violation. The circuits were being pulled from the basement into the bottom of a flush mounted panel. There were 16 12-2 circuits, 1 10-3 circuit, and 1 6-2 circuit. All of these wires were squeezed into a 4 ft. piece of 2 inch pvc conduit. I don't see how he got them in. Had to use soap! Thanks to all for the input.
P.S. The gentleman had a restricted license good for only 200 amp services. The house has a 600 amp service.


#86004 - 08/28/03 01:05 AM Re: code question  
Big Jim  Offline
Member
Joined: Jul 2003
Posts: 394
Denver, CO USA
I'm curious. How big does a house have to be to need a 600 amp service? (asks me, crusing by on 125)


#86005 - 08/28/03 06:24 AM Re: code question  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
Big Jim, I am starting to trim out a house that has a 600 amp service, Its 14,000 sq ft! Also has 25 ton of a/c in it.


Shoot first, apologize later.....maybe

#86006 - 08/28/03 11:19 AM Re: code question  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Ron,

312.5(C)(g) doesn't say anything about the conduit being installed as a system. The entire exception expects the conduit to not connect to anything at the top & if thats the case, why bother putting in part g of the exception?

The use of conduit for this type of installation is rarely done for protection, it is for apperance, so I don't think Note 2 to table 1 of chapter 9 applies.

Of course, I've been totally out in left field before.

Anyone else have an opinion on this?


Few things are harder to put up with than the annoyance of a good example.

Page 1 of 2 1 2

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.8161 MB (Peak: 0.9926 MB) Zlib enabled. Server Time: 2017-05-25 06:44:22 UTC