Is This Receptacle Wired Correctly? #85544
07/13/03 06:50 PM
07/13/03 06:50 PM
T
ThinkGood  Offline OP
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Here is a 20A, 250V receptacle (6-20R):
[Linked Image]

In my house, there is one that was wired using "BX" 10-3. (It's either type AC or type MC, black/red/white, no separate ground conductor.) At the device, the black and red connect to the two hot terminals, respectively. The white connects to the ground terminal.

At the panel, the black and red connect to two 20A breakers, with the common trip (is that the term?) so if one trips, the other does as well. The white is connected to the neutral bus bar.

Do you see any problem with this?

2017 / 2014 NEC & Related Books and Study Guides
Re: Is This Receptacle Wired Correctly? #85545
07/13/03 07:28 PM
07/13/03 07:28 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
If the panel this receptacle is being fed from is your main service panel I don't see much of a problem other than the wire should be green and there should also be a pigtail to the box. If the panel is a sub panel then there is a problem. By connecting the equipment ground of the receptacle to the neutral buss in the sub panel you have created a parallel neutral path for the sub panel path back to the service panel using the armor of the BX cable. The neutral wire should be disconnected from the receptacle and capped off then a jumper installed from the metal box to the receptacle.

Curt


Curt Swartz
Re: Is This Receptacle Wired Correctly? #85546
07/13/03 09:24 PM
07/13/03 09:24 PM
T
ThinkGood  Offline OP
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Curt:

The panel is the main panel. I was thinking along the same lines, that perhaps there is a risk of parallel paths.

If it's not an issue (the neutral and ground bars are bonded inside the panel) then that's great.

Thanks.

Re: Is This Receptacle Wired Correctly? #85547
07/14/03 06:40 PM
07/14/03 06:40 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 785
Oradell NJ USA
If the white wire is reidentified as green at both ends (socket and panel) and in the panel it is connected to the equipment ground (that the right term for the green wire and metal case of the panel?) that the bare grounds from
romex runs connect to, that should be fine, yes?

Re: Is This Receptacle Wired Correctly? #85548
07/15/03 10:19 PM
07/15/03 10:19 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
I recently encountered this issue with a 220v (2-pole) GFI breaker. Guess what? The wire that I always thought was a neutral turned out to be a ground instead- the GFI set me right!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,917
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,537 Are you busy
180,340 Re: Forum
170,829 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9667 MB (Peak: 1.1038 MB) Zlib enabled. Server Time: 2018-01-18 14:09:21 UTC