#85544 - 07/13/03 07:50 PM Is This Receptacle Wired Correctly?  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Here is a 20A, 250V receptacle (6-20R):
[Linked Image]

In my house, there is one that was wired using "BX" 10-3. (It's either type AC or type MC, black/red/white, no separate ground conductor.) At the device, the black and red connect to the two hot terminals, respectively. The white connects to the ground terminal.

At the panel, the black and red connect to two 20A breakers, with the common trip (is that the term?) so if one trips, the other does as well. The white is connected to the neutral bus bar.

Do you see any problem with this?


2017 / 2014 NEC & Related Books and Study Guides

#85545 - 07/13/03 08:28 PM Re: Is This Receptacle Wired Correctly?  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
If the panel this receptacle is being fed from is your main service panel I don't see much of a problem other than the wire should be green and there should also be a pigtail to the box. If the panel is a sub panel then there is a problem. By connecting the equipment ground of the receptacle to the neutral buss in the sub panel you have created a parallel neutral path for the sub panel path back to the service panel using the armor of the BX cable. The neutral wire should be disconnected from the receptacle and capped off then a jumper installed from the metal box to the receptacle.

Curt


Curt Swartz

#85546 - 07/13/03 10:24 PM Re: Is This Receptacle Wired Correctly?  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Curt:

The panel is the main panel. I was thinking along the same lines, that perhaps there is a risk of parallel paths.

If it's not an issue (the neutral and ground bars are bonded inside the panel) then that's great.

Thanks.


#85547 - 07/14/03 07:40 PM Re: Is This Receptacle Wired Correctly?  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
If the white wire is reidentified as green at both ends (socket and panel) and in the panel it is connected to the equipment ground (that the right term for the green wire and metal case of the panel?) that the bare grounds from
romex runs connect to, that should be fine, yes?


#85548 - 07/15/03 11:19 PM Re: Is This Receptacle Wired Correctly?  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
I recently encountered this issue with a 220v (2-pole) GFI breaker. Guess what? The wire that I always thought was a neutral turned out to be a ground instead- the GFI set me right!



Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7682 MB (Peak: 0.9058 MB) Zlib enabled. Server Time: 2017-07-23 02:55:44 UTC