Landscape Lights In Pvc #85539
07/12/03 06:29 PM
07/12/03 06:29 PM
R
Ron100  Offline OP
Junior Member
Joined: Jul 2003
Posts: 1
Burlingame, CA, USA
LANDSCAPE LIGHTING USING PVC: 120 volt 20 amp GFCI protected: 12 inches (plus) depth: Lights in lawn aside concrete walkway:

Question: Do sweeps and risers to boxes at grade need to be rigid metallic (galvanized)?

Many thanks, Ron

2017 / 2014 NEC & Related Books and Study Guides
Re: Landscape Lights In Pvc #85540
07/12/03 08:06 PM
07/12/03 08:06 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Are you referring to possible physical damage? per 352.12(C)?

Re: Landscape Lights In Pvc #85541
11/04/03 08:07 PM
11/04/03 08:07 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I Can't use PVC where I'm at, (Galvy Only!)but out of town in other cities in my area... Direct burial romex, sleaved with PVC, or just PVC all the way. Then, I dig, ( Or, should I say, have some of the generals guys dig. )a post hole at each light location. Mount my box to a pressure treated 2x4, with a 45 at the top. Looks nice, like it was supposed to be there! Then have the general fill the post hole with concrete, around the 2x4, and the sleeve or conduit. Once the concrete is dry, it is a solid unit! Sounds like a bit too much, but practically in-destructable. You have to run over it with a truck!

But, to answer your question. You still need to support the box, and it depends on what is allowed in your area. Call your Inspector.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Landscape Lights In Pvc #85542
11/06/03 05:56 AM
11/06/03 05:56 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
Q on that e57, could each box be buried ?

Re: Landscape Lights In Pvc #85543
11/06/03 06:15 AM
11/06/03 06:15 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Ron if you want to support a box holding a fixture with the raceway it must be with rigid and you must follow the rules of 314.23(F)

Quote
314.23(F) Raceway Supported Enclosures, with Devices, Luminaires (Fixtures), or Lampholders. An enclosure that contains a device(s) or supports a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 450 mm (18 in.) of the enclosure.


If you want to stay with PVC you will have to support the box some other way.

And then of course the inspector could get you on exposed to physical damage as Redsy has pointed out.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,547 Are you busy
180,353 Re: Forum
170,835 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.006s) Memory: 0.9670 MB (Peak: 1.1059 MB) Zlib enabled. Server Time: 2018-01-19 11:32:09 UTC