#85479 - 07/08/03 12:42 AM PVC Wet location??  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
I hdd a subpanel feed about 60 feet under ground in PVC. Inspector did not pass because the 2-3 that was pulled through the PVC not wet location rated. Is the inside of the PVC wet location??

Edward


Thanks
Edward

2017 / 2014 NEC & Related Books and Study Guides

#85480 - 07/08/03 01:46 AM Re: PVC Wet location??  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
Edward, from the 99 NEC Article 100-Locations- "Wet Locations. Installations underground or in concrete slabs or masonry in direct contact with the earth, and locations subject to saturation with water or other liquids, such as vehicle washing areas, and locations exposed to weather and unprotected."
If it's in the ground, it's a wet location.


#85481 - 07/08/03 04:59 AM Re: PVC Wet location??  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
From the 2002 NEC

Quote

300.5(D)(5) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.


And the definition of Wet location is the same as stamcom put up from the 99 code.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#85482 - 07/08/03 05:58 AM Re: PVC Wet location??  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Edward
Alot of the conductors today come with a THHN/THWN rating, where the rating of the conductor is 90 degrees (column 3, table 310.16) if you use it as THHN, or 75 degrees (column 2, table 310.16) if you use it for THWN. The THWN is permitted for wet locations at 75 degrees. I am curious as to what conductor type you did use?

Pierre


Pierre Belarge

#85483 - 07/08/03 09:40 AM Re: PVC Wet location??  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
To add to comments already posted… In many regions, underground raceways breath and accumulate moisture, no matter how much “sealing” is attempted. If “2-3” is a multiconductor cable, it’s unlikely that the individual conductors (or the outer cable jacket) are labeled for wet locations—like you would find with XHHW or USE/RHW conductors.


#85484 - 07/11/03 07:48 AM Re: PVC Wet location??  
pip  Offline
Member
Joined: Dec 2000
Posts: 15
Little Elm,Tx
The only way to keep water out of any conduit
with fitttings underground is to pressurize it. I live in dallas,tx and have never pulled wire out of an exsiting conduit underground that was not completely full of water.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7760 MB (Peak: 0.9226 MB) Zlib enabled. Server Time: 2017-07-25 12:44:55 UTC