Engineering Supervision #85462
07/07/03 03:28 PM
07/07/03 03:28 PM
M
mountainman  Offline OP
Member
Joined: Jan 2002
Posts: 54
Richmond Va. U.S.A.
Article 310-15(b) of the 1996 NEC Engineering supervision, an engineer states that with his calculations he can use 4-4/0 conductors on a 4 wire wye circuit with a 225 ampere over currant protection. Would this override 310-15 Note #10(c). He has 4/0 copper in EMT in an electric room. And would you rquire the engineer to show his calculations? Thanks Joe

2017 / 2014 NEC & Related Books and Study Guides
Re: Engineering Supervision #85463
07/07/03 04:10 PM
07/07/03 04:10 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
As the AHJ, an engineer has the responsibility to adequately demonstrate to you that the cable installation conforms to article 310. Paper calculations submitted to you containing a suitable explanation and his PE stamp may adequately support his position to your satisfaction.




[This message has been edited by Bjarney (edited 07-08-2003).]

Re: Engineering Supervision #85464
07/07/03 05:50 PM
07/07/03 05:50 PM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
mountainman ---

If you are inspecting and is is not building according to the perscriptive code, you should ask for his calculations.

You need to have someone who can tell if the computations are correct or not.

Re: Engineering Supervision #85465
07/07/03 08:12 PM
07/07/03 08:12 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Absolutely have him/her show calculations and sign/seal them.
But, what am I missing? Table 310-16 shows 4/0 CU in the 75 degree column to have an ampacity of 230A. What is the issue with 225A CB serving a 230A conductor? Is it 100% rated breaker or something else? Maybe aluminum?

[This message has been edited by Ron (edited 07-07-2003).]


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,360 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.9579 MB (Peak: 1.0913 MB) Zlib enabled. Server Time: 2018-01-19 22:47:42 UTC