MC cables to conduit wiring #85281
06/15/03 02:54 AM
06/15/03 02:54 AM
N
Nagelec  Offline OP
Member
Joined: Jun 2003
Posts: 12
Sharjah, UAE
We intend to use the MC (Metal clad) cable on cable trays in the existing offshore platform which has presently the conduit installations. I would like to know how the MC cable (Aluminium sheathed) shall enter from Div.1 area into the MCC room (safe area). All the entries to the existing MCC room is as conduit entry. Can any one please clarify how this conversion (Cable to conduit)takes place?

2017 / 2014 NEC & Related Books and Study Guides
Re: MC cables to conduit wiring #85282
06/15/03 10:15 AM
06/15/03 10:15 AM
E
elektrikguy  Offline
Member
Joined: May 2002
Posts: 132
woodstock,ga,usa
A box?

Re: MC cables to conduit wiring #85283
06/24/03 09:12 PM
06/24/03 09:12 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
If the wires are continuous, without a splice, it is possible to connect the MC to the seal fitting (outside the zone).

Re: MC cables to conduit wiring #85284
06/24/03 11:41 PM
06/24/03 11:41 PM
N
Nagelec  Offline OP
Member
Joined: Jun 2003
Posts: 12
Sharjah, UAE
Hi John Steinke,

We don't want to splice the cable while entering into the false flooring of MCC room. The MCC room has a false false flooring and the MCC /DBs are installed on the false flooring tiles. From the cellar deck (lower deck), which is classified as Class I, Div 1 area, the MC cable has to enter the false flooring first and after a small run on the cable trays in the false flooring, it will be terminated in the MCC.
Our problem is how to enter the false flooring from a Div 1 area i.e. through conduit or through Muti cable transits? The MC cables are installed on cable trays in the cellar deck. So if the entry is through conduit, then what area all the fittings to be considered?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,264
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,587 Are you busy
180,382 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.9575 MB (Peak: 1.0896 MB) Zlib enabled. Server Time: 2018-01-22 04:41:10 UTC