#85053 - 05/24/03 06:30 PM Is this a permitted method emt to ac?  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
Is this allowed? Assume that there are no splices in the wires (that the BX sheath was cut several feet into its length and the newly exposed wire now resides in the emt. Also, do I need to keep the cover plate on the pull box accessible after it's installed in the house?

[img}http://home.netcom.com/~wa2ise/power/emt-bx.jpg[/img]

Bob, homeowner who'd like to get it right.


2017 / 2014 NEC & Related Books and Study Guides

#85054 - 05/24/03 06:32 PM Re: Is this a permitted method emt to ac?  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
[Linked Image]


#85055 - 05/25/03 06:44 PM Re: Is this a permitted method emt to ac?  
WebSparky  Offline
Member
Joined: Feb 2003
Posts: 138
Cleveland, Ohio
Quote
Also, do I need to keep the cover plate on the pull box accessible after it's installed in the house?


Nec 2002
314.29 Boxes and Conduit Bodies to Be Accessible.
Boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building...........

Hope this helps!
Dave


Dave

#85056 - 05/25/03 11:56 PM Re: Is this a permitted method emt to ac?  
Gabriel  Offline
Junior Member
Joined: May 2003
Posts: 5
Cedar Rapids, IA usa
Hello Bob,

Yep-Conduit bodies and covers have to be accesible however if you change that jake-L in your photo to a flex changeover (maybe 1/2 rigid coupling) I believe your good to go
Also, all three items in the photo are approved raceways, I surely haven't ever heard of anything against using all together!


#85057 - 05/26/03 09:04 AM Re: Is this a permitted method emt to ac?  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
If you were to change the pull elbow to a rigid coupling, it doesn't appear that one could see the required anti-short bushing for inspection purposes. The fix for that would be to use the type of AC connector with the small hole through which the bushing can be seen.
I think you're fine as is, provided you make sure it's accessible...S

[This message has been edited by electure (edited 05-26-2003).]


#85058 - 05/26/03 10:26 AM Re: Is this a permitted method emt to ac?  
elektrikguy  Offline
Member
Joined: May 2002
Posts: 132
woodstock,ga,usa
If the inspector was looking for an antishort all he would have to do is remove the cover and look for the little tail on the antishort. I have used a similar method when roughing in block walls. I would extend 1/2" conduits and 90 at ceiling. One could run mc to the conduit, use a mc/emt connector and strip mc long enough to get to box.


#85059 - 05/28/03 11:30 PM Re: Is this a permitted method emt to ac?  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Wire that is not a part of a UL approved NEC wiring method is required to be marked with certain information every so many feet. Since wire used in AC cable is typically not marked and only the tag on the AC cable tells you what type and size wire it is, technically I think it may be noncompliant.

Practically I think it is probably ok.

AC cable is not a raceway by the way.

No the short radius elbow cannot be buried.



Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.004s) Memory: 0.7850 MB (Peak: 0.9396 MB) Zlib enabled. Server Time: 2017-05-28 06:30:30 UTC