Green or Green With Yellow Stripe for EGC Only!! #84991
05/22/03 09:34 AM
05/22/03 09:34 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
The 2005 NEC will include a new requirement stating that green insulation or green with a yellow stripe are only permitted to be used for the identification of the equipment grounding conductor.

[Linked Image]



[This message has been edited by Joe Tedesco (edited 05-25-2003).]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Green or Green With Yellow Stripe for EGC Only!! #84992
05/22/03 11:00 AM
05/22/03 11:00 AM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
.

[This message has been edited by dana1028 (edited 05-22-2003).]

Re: Green or Green With Yellow Stripe for EGC Only!! #84993
05/22/03 12:27 PM
05/22/03 12:27 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The proposed wording says that any conductor "identified as permitted" in this section shall
only be used as an EGC. The use of a bare wire is permitted to identify an EGC, this will mean that bare conductors are no longer permitted to be used as grounding electrode conductors.
Don


Don(resqcapt19)
Re: Green or Green With Yellow Stripe for EGC Only!! #84994
05/22/03 12:55 PM
05/22/03 12:55 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Is there a similar proposal for white and white/red colors with grounded-circuit conductors?

The hazards seem similar to those cited by Phil Simmons for green and green/yellow.

Re: Green or Green With Yellow Stripe for EGC Only!! #84995
05/22/03 02:42 PM
05/22/03 02:42 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Don:

I think that the new sentence makes it clear that the color green or green with a yellow strip will not be allowed to be used to identify the GEC.

The comment stage is where any changes proposed to the original accepted actions can be made by any person who wants to send one in.



[This message has been edited by Joe Tedesco (edited 05-24-2003).]


Joe Tedesco, NEC Consultant
Re: Green or Green With Yellow Stripe for EGC Only!! #84996
05/22/03 02:47 PM
05/22/03 02:47 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
What would we do with all that bare solid larger than #10? [Linked Image]

Roger

Re: Green or Green With Yellow Stripe for EGC Only!! #84997
05/22/03 03:08 PM
05/22/03 03:08 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
So then an exception to the rule above may be in order"

"Exception: Grounding electrode conductors shall be permitted to be bare."


Joe Tedesco, NEC Consultant
Re: Green or Green With Yellow Stripe for EGC Only!! #84998
05/22/03 03:25 PM
05/22/03 03:25 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
Who would this change benifit?

Re: Green or Green With Yellow Stripe for EGC Only!! #84999
05/22/03 03:32 PM
05/22/03 03:32 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Joe,
You are correct that the new wording would prohibit the use of green for the grounding electrode conductor. My comment will be to "accept in principle" with the following words added at the end of the proposed wording, "or grounding electrode conductor".
Don


Don(resqcapt19)
Re: Green or Green With Yellow Stripe for EGC Only!! #85000
05/22/03 04:04 PM
05/22/03 04:04 PM
C
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
Why not identify the EGC with green and yellow stripes only and the GEC with green (or bare) only. Then the US would follow the international standard on the EGC identification [Linked Image] (I don't think there is a standard for the GEC)

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 1.0248 MB (Peak: 1.2026 MB) Zlib enabled. Server Time: 2018-01-18 23:26:11 UTC