ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 136 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#84853 05/12/03 06:50 PM
Joined: Jan 2002
Posts: 1,457
E
Member
I am wiring a home theater and the equipment will be installed in the basement on a rack. The specs call for two 20 amp isolated ground receptacles. The basement is not finished and the rack will be in front of the receptacles. I am not sure if these are required to be gfi protected under the exceptions to 210.8 A (5). I don't think so but I'd like other opinions. Thanks Scott

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84854 05/12/03 07:13 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
I would think both exception No. 1 and No. 2 would apply.

Quote
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(A) Dwelling Units.

(5) Unfinished basements

Exception No. 1: Receptacles that are not readily accessible.

Exception No. 2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8)
.


Isolated ground, isolated from what in a typical residence?

If you run it in NM from a main panel it will be isolated, as long as you don't mount the box to a water pipe. [Linked Image]

But if the customer thinks it is better what can you do.


Bob Badger
Construction & Maintenance Electrician
Massachusetts