Undersized neutral???? #84458
04/02/03 03:07 AM
04/02/03 03:07 AM
N
nykr95  Offline OP
Junior Member
Joined: Apr 2003
Posts: 2
Hi!

I recently replace an existing 30AMP 2 Pole with a 30AMP 2 Pole GFCI on my main panel. This breaker services my pool equipment - which are mostly 240 but also have some 120 lights and misc equip. I noticed that the 2 hot conductors are either #8 or #10 copper but the neutral (white) is #12. Is this normal? Is there a chance that it can overheat? Can it effect the voltage since the drop is about 100 feet? If necessary what can be done to remedy the situation other than pulling a new neutral conductor?

2017 / 2014 NEC & Related Books and Study Guides
Re: Undersized neutral???? #84459
04/02/03 08:51 AM
04/02/03 08:51 AM
G
GEO  Offline
Member
Joined: Mar 2003
Posts: 47
Lancaster,Pa
is it a main or branch(feeding 1 piece of equipment)breaker? GEO

Re: Undersized neutral???? #84460
04/02/03 08:54 AM
04/02/03 08:54 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
I commend you for installing the GFI, but without further information about your equipment, none of us can safely make a call on this.
I'd suggest you hire a qualified, licensed electrician to check this out for you.

Re: Undersized neutral???? #84461
04/02/03 03:06 PM
04/02/03 03:06 PM
N
nykr95  Offline OP
Junior Member
Joined: Apr 2003
Posts: 2
My friend who is a licensed electrician will be coming out this weekend to look at it. I also checked the voltages at the pool pump - and found it is 175V - while it is 240V at the Main panel. Isn't that an awful high voltage drop? Its about a 100 foot run.

Re: Undersized neutral???? #84462
04/03/03 08:48 PM
04/03/03 08:48 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
It's time for a pro to look at your set-up. That is way too much voltage drop- I'm guessing that there is another problem waiting to be found. Voltage drop, under load, should not exceed 5%. A 240 v. motor should not be run at less than 204 V.
In theory, it is sometimes permissible to reduce the size of the neutral. For a 30 amp circuit, however, you are required to use a full-size (#10) neutral. Also, the use of different size wires is likely to cause GFI problems.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,508 Are you busy
180,293 Re: Forum
170,798 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.041s Queries: 14 (0.019s) Memory: 0.9660 MB (Peak: 1.1041 MB) Zlib enabled. Server Time: 2018-01-16 09:57:06 UTC