#84187 - 03/14/03 12:26 PM Panelboards in clothes closet  
steve66  Offline
Member
Joined: Mar 2003
Posts: 25
Can a panelboard be placed in a clothes closet? I know 240.24D says overcurrent devices cannot be located in the vicinity of easily ignitible material, such as clothes closets. But, there isn't any similar restriction in article 408 - Switchboards and Panelboards. Is it possible 240.24 doesn't apply since the panelboard would contain any sparks or flames created by a breaker?


2017 / 2014 NEC & Related Books and Study Guides

#84188 - 03/14/03 01:57 PM Re: Panelboards in clothes closet  
boxford  Offline
Member
Joined: Mar 2003
Posts: 15
St. Paul, MN, USA
Steve,

You have answered your own question. Article 408.2 states the following:

408.2 Other Articles. Switches, circuit breakers, and over-current devices used on switchboards, panelboards, and distribution boards, and their enclosures, shall comply with this article and also with the requirements of Articles 240, 250, 312, 314, 404, and other articles that apply. Switchboards and panelboards in hazardous (classified) locations shall comply with the requirements of Articles 500 through 517.

So, the panelboard cannot be located in the clothes closet because of Article 240.24(D).

Brian


#84189 - 03/14/03 02:42 PM Re: Panelboards in clothes closet  
steve66  Offline
Member
Joined: Mar 2003
Posts: 25
Yes, that does seem to make it pretty clear.
Thanks.


#84190 - 03/17/03 07:46 PM Re: Panelboards in clothes closet  
steve66  Offline
Member
Joined: Mar 2003
Posts: 25
Well, I thought that was a closed topic. Then I ran across Article 240.30A, "Protection from physical damage". This states overcurrent devices shall be protected from damage by:
1) installation in an enclosure, ect.
2) installation on an open type switchboard, ect. free from easily ignitible material.

(I've taken the liberty to shorten the exact text some.) My point is, installation in enclosures doesn't say anything about the area around the enclosure being free from ignitible material. In addition, the handbook says "overcurrent devices enclosed in cabinets or cutout boxes ensure that hot metal particles will not be ejected in the vicinity of combustible material".

So, I'm still wondering, can a panelboard go in a closet, or not?


#84191 - 03/17/03 08:55 PM Re: Panelboards in clothes closet  
George  Offline
Member
Joined: Feb 2002
Posts: 375
steve66 ---

I don't think anyone could argue this issue is rationally based.

Most breaker boxes here are in garages. Think 40gal of explosive liquids.

and a lot of clothes closets are small rooms with the clothes in cupboards.

I think the intent is good. I just don't understand the implementation from time to time.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7678 MB (Peak: 0.9080 MB) Zlib enabled. Server Time: 2017-07-28 17:04:08 UTC