sub panel main #84135
03/11/03 05:01 PM
03/11/03 05:01 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
When is a main breaker required in a sub panel in a residential detached garage? Aso what is the min. feeder ampacity for 3 circuits?

2017 / 2014 NEC & Related Books and Study Guides
Re: sub panel main #84136
03/11/03 08:11 PM
03/11/03 08:11 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
gserve,
Consider the following:
408.16 Overcurrent Protection.
(A) Lighting and Appliance Branch-Circuit Panelboard Individually Protected.
Each lighting and appliance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard.
Exception No. 1: Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard.
I'm sure the exception will work for you. As far as the ampacity of the feeder is concerned, I can't tell you anything without knowing the rating of the branch circuits.
Hope it helps,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
Re: sub panel main #84137
03/11/03 08:27 PM
03/11/03 08:27 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Don't forget that 225.31 requires a disconnect at the detached garage. 225.33 permits up to 6 breakers to serve as the required disconnect. 225.39(D) requires that the feeder disconnecting means have a rating of not less than 60 amps for this application. Note that the section does not actually require a 60 amps feeder, but only a 60 amp disconnecting means. I think that the intent was to require a 60 amp feeder circuit, but the code words don't actually say that.
Don


Don(resqcapt19)
Re: sub panel main #84138
03/11/03 08:37 PM
03/11/03 08:37 PM
W
WebSparky  Offline
Member
Joined: Feb 2003
Posts: 138
Cleveland, Ohio
Don't forget the grounding electrode!

And GFCI's!


Dave
Re: sub panel main #84139
03/11/03 08:49 PM
03/11/03 08:49 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
The branch circuits are 1 15A lighting 1 20A receptacle and 1 20A 240V air compresser

Re: sub panel main #84140
03/11/03 08:56 PM
03/11/03 08:56 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
Speaking of the elctrodes can I use the main service electrodes which are about 15' away from the garage without driving additional electrodes for the garage GES?

Re: sub panel main #84141
03/12/03 10:25 PM
03/12/03 10:25 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
I can dig it Don. So, gserve, you could set a small load center with 6 breaker spaces or less (if they make one less than 6 spaces), and not need to have a disconnect. If you want to add a panel of any greater size (in terms of breaker space), as Don pointed out, you're going to have to add a main, which can serve as a disconnect, or add a disconnect.
Regards,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
Re: sub panel main #84142
03/12/03 10:52 PM
03/12/03 10:52 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Doc,
The six disconnect rule is not based on the number of spaces in the panel, but the number of breakers installed. Just because it is possible to install more breakers in the future, doesn't make it a violation today.
Don


Don(resqcapt19)
Re: sub panel main #84143
03/13/03 07:59 PM
03/13/03 07:59 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
I'm with you Don. The reason I mentioned it, is because a friend of mine ran into this problem. He had some AHJ hammer him for it. The AHJ's was trying to prevent additional disconnects from being added in the future. My response was....How does he know that you won't add 2 pole breakers for other equipment, and therefore need a 12 space panel? (it was a single phase application) My buddy replied, "Who know's?"
So, let me retract my earlier statement, and say, "Based on some prior experience that a friend of mine had, be prepared, gserve, for the possibility that an AHJ, may walk onto your project, and want assurance that you, or someone in the future will not add breakers in that MLO panel, which would be a violation." So, gserve, it might be a good idea to give them a call, and see what kind of response you get from them.

Trying to be helpful,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.9996 MB (Peak: 1.1673 MB) Zlib enabled. Server Time: 2018-01-17 07:09:27 UTC