Current Carrying Conductors #84102
03/10/03 09:40 AM
03/10/03 09:40 AM
B
boxford  Offline OP
Member
Joined: Mar 2003
Posts: 15
St. Paul, MN, USA
I work for 3M as an electrical engineer and during a design review we had a debate on what is exactly considered a current carrying conductor for the purpose of derating, pertaining to T310.15(B)(2)(a). A standard I/O module is only rated for 2A and is typically fused at 5A. So most of the devices connected to an I/O module such as a solenoid valve, a level switch, a proximity switch, etc. has very little current flowing through the conductors connected to that device. Is there a specific article, section, or exception in the code that states certain devices do not have to be considered current carrying conductors when derating. Any help that you can offer in this issue would be greatly appreciated.

2017 / 2014 NEC & Related Books and Study Guides
Re: Current Carrying Conductors #84103
03/10/03 10:34 AM
03/10/03 10:34 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Look at Exception #1 to 310.15(B)(2).
Don


Don(resqcapt19)
Re: Current Carrying Conductors #84104
03/10/03 02:03 PM
03/10/03 02:03 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
NFPA70 (the NEC) is for premises wiring not for machinery. NFPA79 (Electrical Standard for Industrial Machinery) may be more appropiate for your application. The scope of NFPA79 includes: "...systems of industrial machines...commencing at the place of connection of the supply..."

Some major differences between the two standards:
minimum circuit wire size; NEC-#14, NFPA79-#24 (in raceway)
maximum raceway fill; NEC-40%, NFPA79-50%
drain holes in raceways; NEC-not allowed, NFPA79- upto 1/4"
raceway as grounding or bonding conductor; NEC-allowed; NFPA70 - not allowed

[This message has been edited by JBD (edited 03-10-2003).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,508 Are you busy
180,291 Re: Forum
170,798 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.007s) Memory: 0.9497 MB (Peak: 1.0733 MB) Zlib enabled. Server Time: 2018-01-16 07:17:22 UTC