#84102 - 03/10/03 10:40 AM Current Carrying Conductors  
boxford  Offline
Member
Joined: Mar 2003
Posts: 15
St. Paul, MN, USA
I work for 3M as an electrical engineer and during a design review we had a debate on what is exactly considered a current carrying conductor for the purpose of derating, pertaining to T310.15(B)(2)(a). A standard I/O module is only rated for 2A and is typically fused at 5A. So most of the devices connected to an I/O module such as a solenoid valve, a level switch, a proximity switch, etc. has very little current flowing through the conductors connected to that device. Is there a specific article, section, or exception in the code that states certain devices do not have to be considered current carrying conductors when derating. Any help that you can offer in this issue would be greatly appreciated.


2017 / 2014 NEC & Related Books and Study Guides

#84103 - 03/10/03 11:34 AM Re: Current Carrying Conductors  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Look at Exception #1 to 310.15(B)(2).
Don


Don(resqcapt19)

#84104 - 03/10/03 03:03 PM Re: Current Carrying Conductors  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
NFPA70 (the NEC) is for premises wiring not for machinery. NFPA79 (Electrical Standard for Industrial Machinery) may be more appropiate for your application. The scope of NFPA79 includes: "...systems of industrial machines...commencing at the place of connection of the supply..."

Some major differences between the two standards:
minimum circuit wire size; NEC-#14, NFPA79-#24 (in raceway)
maximum raceway fill; NEC-40%, NFPA79-50%
drain holes in raceways; NEC-not allowed, NFPA79- upto 1/4"
raceway as grounding or bonding conductor; NEC-allowed; NFPA70 - not allowed

[This message has been edited by JBD (edited 03-10-2003).]



Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,853
Joined: April 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.7518 MB (Peak: 0.8759 MB) Zlib enabled. Server Time: 2017-07-22 06:55:02 UTC