load calculations #84088
03/09/03 04:57 PM
03/09/03 04:57 PM
E
elecbob  Offline OP
Member
Joined: Aug 2002
Posts: 141
WA
I did some load calcs for a residential triplex. Each unit totalled 50 amps. The house load was 55 amps. The service load totalled 174 amps. The building is in an undergrounded area and the only service voltage available is 480 volts, single phase. I want to install:
A 100 amp 480 volt safety switch.
A 50 KVA transformer to supply the 120/240 volts.
A meter pack rated at 200 amps.
4 - 60 amp panels.
Think it will fly?
Thanks Bob

2017 / 2014 NEC & Related Books and Study Guides
Re: load calculations #84089
03/09/03 07:34 PM
03/09/03 07:34 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Bob, Are you saying that the utility will not supply you with a 120/240 volt service?

The only way I can imagine a utility accepting an installation as you described is to install a 480 volt meter before the disconnect and transformer then have 4 customer read meters on the secondary side of the transformer. How would the utility control future un-metered loads being connected to the disconnect or transformer?

Curt


Curt Swartz
Re: load calculations #84090
03/09/03 10:15 PM
03/09/03 10:15 PM
E
elecbob  Offline OP
Member
Joined: Aug 2002
Posts: 141
WA
I erred on this one. The utility wants to install a pad mounted transformer on a 48" by 56" pad in the back yard. Not good. My option is to install a meter ahead of my own transformer in the basement. I couldn't seperately meter the units but the heat and hot water are central so it shouldn't be a big deal. Not the best solution but cheaper and more doable.
bob
[This message has been edited by elecbob (edited 03-09-2003).]

[This message has been edited by elecbob (edited 03-10-2003).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,592 Are you busy
180,388 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9496 MB (Peak: 1.0743 MB) Zlib enabled. Server Time: 2018-01-22 09:54:24 UTC