#83180 - 01/17/03 09:32 AM 300amp main blew apart?????  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Hello all, Wanted some education from the guro`s We had a 300a main just blow apart internally it appears yesterday.No one was injured thanks to the right hand turn on and turn away method.We meged all the lines and couldn`t find a problem anywhere. This circuit had been off for approx. 30-40 days.The area is not moist or damp, humidity maybe. It was a square D big frame I don`t have all info in front of me.If you guys could help shed some light on this it would be much appreciated.PS one of the crew already figured it out he says sh** Happens.Maybe he`s right but I figure we can do better.


2017 / 2014 NEC & Related Books and Study Guides

#83181 - 01/17/03 07:58 PM Re: 300amp main blew apart?????  
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
Anything man made is subject to failure unfortunately. Maybe since the breaker is not swiped that often the tripping mechanism was stiff or ceassed and a load elsewhere in the building called for the main to trip and since it could not it blew apart from the force (high ampacity) of the short circuit. It could be anything. Maybe your man is right it just simply failed.


#83182 - 01/17/03 09:33 PM Re: 300amp main blew apart?????  
txsparky  Offline
Member
Joined: May 2001
Posts: 552
Magnolia,.Texas U.S.A.
Since it had been off for 30 or 40 days,I assume you must have been doing work downstream of the main.Were the lines you mentioned megged prior to turning on the switch? It could be possible that you had a fault that cleared itself once you energized it.


Donnie

#83183 - 01/18/03 12:07 AM Re: 300amp main blew apart?????  
lighthouse  Offline
Member
Joined: Jan 2003
Posts: 134
philadelphia pa 19125
Reel-Break...with the eguipment off for 30-40 days is there anyway a rat or modent could have gotting in there.we had a 13.2 outside switchgear.and the rats would trip out the gear 2 or 3 times a year.no more rat.

glad to hear no one got hurt.


#83184 - 01/18/03 05:50 PM Re: 300amp main blew apart?????  
jes  Offline
Member
Joined: Jul 2002
Posts: 103
CT
Were you closing on a load or just an open circuit say to a DP with all breakers off?


#83185 - 01/18/03 09:15 PM Re: 300amp main blew apart?????  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Please explain the "right hand turn on and turn away method" as it sounds to have done its job in this case.


#83186 - 01/18/03 10:37 PM Re: 300amp main blew apart?????  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
ThinkGood,

The method for closing breakers is to reach for the handle, then turn away from the panel with the breaker behind you. Don't look at it. Throw the handle.

This way, any arc-flash is likely to not injure your face, and one tends to run when things are exploding around them, so having your feet facing away from the panel will keep one from running into the arc-flash.

Make sense?

Being left handed, I'm not sure of the significance of using the right hand, unless it is to place less risk on my dominant hand, but that only works for lefties!

Left handed people are in their right mind!

[Linked Image]

-Virgil


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#83187 - 01/20/03 02:07 AM Re: 300amp main blew apart?????  
Len_B  Offline
Member
Joined: Jan 2003
Posts: 53
New Hampshire
I am more familiar with the "left hand rule". As most disconnect operating handles are on the right hand side, the practice is to stand to the right of the enclosure, turn your face away, and operate the device with your left hand. Either way, the fundamentals of staying to the side of harms way, and turning your face (eyes) and feet away from a possible explosion and/or flash are good practice.


#83188 - 01/20/03 10:19 AM Re: 300amp main blew apart?????  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Interesting I`ve always been told the hinges are on the left facing a discon.And thats it`s stronger side. The latches to hold the door closed are on the right. the door if blown open it`s weaker at the left towards the handle so turn on with right hand face away and if blown open the door will hit your forearm aide in head start for the truck.All the breakers or doors I`ve seen have blown open at the door from the handle side where the latches are.All the down stream loads were off when the main was energized thats what puzzled everyone.We had installed a 37.5 kva buck boost to supply an rf dryer but all the disconnects were off and were doulble checked to make sure they were actually off.



Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.002s) Memory: 0.8007 MB (Peak: 0.9665 MB) Zlib enabled. Server Time: 2017-09-25 11:38:26 UTC