Can I Use Cable Ties with MC Cable? #83140
01/14/03 07:07 PM
01/14/03 07:07 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Quote
Joe
I seem to frequently be involved in discussions over the use of cable ties as a supporting means for Metal-Clad Cable. Section 330.30 doesn't clearly state that cable ties can be used as a support method. I am aware that cable ties are clearly defined as a approved method in the following code locations, 320.30 Armored Cable, 334.30 Nonmetallic-Sheathed Cables, 338.10(B)(b) Service-Entrance Cable and 340.10(4). Could you give us your take on this subject?

Thanks


I would have no problem using cable ties, see 330.30 Securing and Supporting.
Type MC cable shall be supported and secured at intervals not exceeding 1.8 m (6 ft).


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Can I Use Cable Ties with MC Cable? #83141
01/14/03 07:21 PM
01/14/03 07:21 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
wasn't it panduit that achieved a listing status for 'support' a while back?

Re: Can I Use Cable Ties with MC Cable? #83142
01/14/03 09:02 PM
01/14/03 09:02 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Joe:
Don't forget the plenum rated tye wrpas for the drop ceiling areas.

John


John
Re: Can I Use Cable Ties with MC Cable? #83143
01/30/03 07:28 PM
01/30/03 07:28 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
FYI: Name-brand wire ties are "annealed" in a glycol bath, which has the effect of doubling their strength. No-name ties may not be so treated.

Re: Can I Use Cable Ties with MC Cable? #83144
01/30/03 09:25 PM
01/30/03 09:25 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Spaces above dropped ceilings used for environmental air are not plenums, see 300.22(C).

A plenum is defined in Article 100

A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system.

I would use metallic types of ties instead of any that are nonmetallic.


Joe Tedesco, NEC Consultant

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,515 Are you busy
180,312 Re: Forum
170,808 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9666 MB (Peak: 1.1050 MB) Zlib enabled. Server Time: 2018-01-17 05:14:26 UTC