New Electrical Loads #82456
11/14/02 07:16 PM
11/14/02 07:16 PM
M
marineEE  Offline OP
Junior Member
Joined: Nov 2002
Posts: 3
Bremerton, WA
I recently gutted an industrial kitchen, replacing several elect appliances with gas, and replacing some 208V appliances with larger 480V appliances. Using article 220-35 to verify the existing service was adequate, I calculated 150kVA (208V) removed from the kitchen and 130kVA (480) installed, for a net reduction in load. According to our local inspector, however, I cannot take credit for any load removed. I must use the maximum demand (last 12 months) times 125% and add the 150kVA of new load! This makes no sense to me!!! My calculations would indicate that I have doubled the kitchen load, when in fact, it has been reduced. Is this tha actual intent of the NEC?!!!

2017 / 2014 NEC & Related Books and Study Guides
Re: New Electrical Loads #82457
11/14/02 07:54 PM
11/14/02 07:54 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
I would submit the plans with a new calculated load for the new remodeled load of the entire building/service. You will have to clearly note the old circuitry and conduits were removed so that the no longer apply.


ed
Re: New Electrical Loads #82458
11/15/02 11:44 AM
11/15/02 11:44 AM
M
marineEE  Offline OP
Junior Member
Joined: Nov 2002
Posts: 3
Bremerton, WA
We considered this, but that means we can't use the 12-month usage as a baseline, and it also means updating panel schedules on about 30 panels for a 20 year old building. That seems like the inspector is simply forcing us to spend a lot of time for a requirement that is NOT the intent of the NEC, nor has any technical requirement.

Re: New Electrical Loads #82459
11/17/02 02:34 AM
11/17/02 02:34 AM
J
Jacuzzi Guy Electric  Offline
Member
Joined: Oct 2002
Posts: 33
Dearborn Heights Michigan Unit...
It's simple:

Your calculated load is 150 kVa. Table 220.11 "all others" 100% demand factor. Do the math, if you have a 480 service, then you must only use 80% of your panel's capacity. So then:

150,000 x 1.25 = 187,500 VA

187,500 VA/480V= 390.625A

Your next available main SVC. is a 400 Amp.

Please let me know if this is any help.

[This message has been edited by Jacuzzi Guy Electric (edited 11-17-2002).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,607 Are you busy
180,425 Re: Forum
170,876 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9578 MB (Peak: 1.0891 MB) Zlib enabled. Server Time: 2018-01-24 11:47:25 UTC