#82328 - 11/05/02 08:59 AM different size breakers on multiwire branch  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
This topic came up on another site. Is it permitted the have a multiwire circuit with a 15 amp on one branch and a 20 amp on the other branch. The neutral is a #12 wire.


2017 / 2014 NEC & Related Books and Study Guides

#82329 - 11/05/02 10:19 AM Re: different size breakers on multiwire branch  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Never thought about it before, but I can't think of a reason not to.
(gut feeling says not to)


#82330 - 11/05/02 12:30 PM Re: different size breakers on multiwire branch  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
I agree Redsy.

210.4(B) requires simultaneous disconnection of the ungrounded conductors that supply stuff on a common yoke. A listed handle tie would take care of that.

I see frequent examples of a 15 A and a 20 A circuit sharing a common 12 gauge neutral in residential systems based on EMT or Flex wiring methods. In this area, 7-county Minneapolis / St. Paul, the age of installation is most commonly 1950 thru the mid-70's. In 1975, the local "all metal" requirement was relaxed to permit NM.

Perhaps the most common configuration was running a general lighting circuit with the laundry circuit.

The slight economic incentive to save on material used is still available in NM if one uses a 12/3 NM homerun with one of the ungrounded 12s on a 15 A breaker, and the rest of the 15 A circuit beyond the 12/3 on 14/2 NM.

Al


Al Hildenbrand

#82331 - 11/05/02 08:37 PM Re: different size breakers on multiwire branch  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
One word of caution would be that you might want to tag the fifteen amp leg of the 12/3 w Gnd in the panel to indicate that it supplies 14 gauge wiring. This is to prevent some follow on genius from supplying the 14 AWG from a replacement 20 amp breaker.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#82332 - 11/08/02 05:13 AM Re: different size breakers on multiwire branch  
Matt M  Offline
Member
Joined: Mar 2001
Posts: 93
Laporte, MN, USA
Just curious, but are there any instances where you would ever want or need to do this? I could maybe see it for a multi-wire that serves a single piece of utilization equipment where it is possible that the loads on each leg are far from equal, but I can't see why you would ever need or want it on a multi-wire for general purpose branch circuits.

Where this would apply to general purpose branch circuits as you suggest, we're talking the difference in price of one single #14 conductor versus the price of one single #12 conductor? Why even bother?


#82333 - 11/08/02 07:14 AM Re: different size breakers on multiwire branch  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
It is not neccesarily the price of the materials that would drive this. I have done it because of the diffculty of running new circuits in an area. I have also used an existing wiring in remodel in this manner. For new construction I probably wouldn't bother.


#82334 - 11/08/02 01:56 PM Re: different size breakers on multiwire branch  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Never done it. Never even thought about. It is just something that came up on another forum.



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7841 MB (Peak: 0.9352 MB) Zlib enabled. Server Time: 2017-07-28 10:59:35 UTC