Feeder to barn. #82320
11/04/02 08:57 AM
11/04/02 08:57 AM
R
Reel-Break  Offline OP
Member
Joined: Apr 2002
Posts: 178
nc
Ran three #4 rhw-2 direct burial cables to a small panel w/2 slots for branch cir. I used 1 hot 1 neu. 1 ground. Separated N and grounding wires.Since only had L1 I jumped it to L2.Is there any code reference to this practice.And also just for info If you use a three phase motor starter on single phase and use all three contacts is this ok.Reason I ask is we wired a paint both it had all three phase cont. w/all contacts being used.What they did was L1 came in through to T1 then jumped back toL2 then t2 and t3 went to motors.L2 came in to L3,Thanks for any code ref #`s I`ll go read.

2017 / 2014 NEC & Related Books and Study Guides
Re: Feeder to barn. #82321
11/04/02 01:09 PM
11/04/02 01:09 PM
E
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Some motor starter manufacturers require all three overload heaters to be installed and carrying current to maintain the ambient temperature inside the overload relay that it was calibrated for.

Ed

Re: Feeder to barn. #82322
11/04/02 07:24 PM
11/04/02 07:24 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Verify that the starter's labeled horsepower rating is suitable/adequate for the served motor. For some starter sizes, this number is often lower than its rating for a given voltage.




[This message has been edited by Bjarney (edited 11-05-2002).]

Re: Feeder to barn. #82323
11/04/02 10:30 PM
11/04/02 10:30 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
ReelBreak:
How did you jump L1 to L2??? If you have two conductors in/under 1 lug, that is a code violation, unless the lug is listed for 2 conductors.
John


John
Re: Feeder to barn. #82324
11/05/02 07:51 AM
11/05/02 07:51 AM
R
Reel-Break  Offline OP
Member
Joined: Apr 2002
Posts: 178
nc
It has lugs out at bottom of panel so L1 goes in at top Jumper goes at bottom of bus bar on the two out lugs.Thats why I ask Is there a violation?I can just leave the jumper off,only have 1 lighting cir on panel.The panel is really over kill but she had it and the larger wire will allow future circuits.When I said barn its more of a shed type not very big.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,592 Are you busy
180,388 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9667 MB (Peak: 1.1054 MB) Zlib enabled. Server Time: 2018-01-22 14:02:45 UTC