ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
Dimmable LED 2x4 lay in fixtures
by HotLine1. 04/24/17 05:43 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,796 Are you busy
169,564 Re: Forum
162,827 Need opinion
Who's Online Now
0 registered members (), 54 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#82320 - 11/04/02 09:57 AM Feeder to barn.  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Ran three #4 rhw-2 direct burial cables to a small panel w/2 slots for branch cir. I used 1 hot 1 neu. 1 ground. Separated N and grounding wires.Since only had L1 I jumped it to L2.Is there any code reference to this practice.And also just for info If you use a three phase motor starter on single phase and use all three contacts is this ok.Reason I ask is we wired a paint both it had all three phase cont. w/all contacts being used.What they did was L1 came in through to T1 then jumped back toL2 then t2 and t3 went to motors.L2 came in to L3,Thanks for any code ref #`s I`ll go read.


2017 / 2014 NEC & Related Books and Study Guides

#82321 - 11/04/02 02:09 PM Re: Feeder to barn.  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Some motor starter manufacturers require all three overload heaters to be installed and carrying current to maintain the ambient temperature inside the overload relay that it was calibrated for.

Ed


#82322 - 11/04/02 08:24 PM Re: Feeder to barn.  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Verify that the starter's labeled horsepower rating is suitable/adequate for the served motor. For some starter sizes, this number is often lower than its rating for a given voltage.




[This message has been edited by Bjarney (edited 11-05-2002).]


#82323 - 11/04/02 11:30 PM Re: Feeder to barn.  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,809
Brick, NJ USA
ReelBreak:
How did you jump L1 to L2??? If you have two conductors in/under 1 lug, that is a code violation, unless the lug is listed for 2 conductors.
John


John

#82324 - 11/05/02 08:51 AM Re: Feeder to barn.  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
It has lugs out at bottom of panel so L1 goes in at top Jumper goes at bottom of bus bar on the two out lugs.Thats why I ask Is there a violation?I can just leave the jumper off,only have 1 lighting cir on panel.The panel is really over kill but she had it and the larger wire will allow future circuits.When I said barn its more of a shed type not very big.



Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7681 MB (Peak: 0.9063 MB) Zlib enabled. Server Time: 2017-04-27 11:08:16 UTC