ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/17/17 10:01 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Generator Cable Sizing
by HotLine1. 10/16/17 07:13 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,356 Are you busy
177,305 Re: Forum
168,931 Need opinion
Who's Online Now
0 registered members (), 39 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#81842 - 09/24/02 09:31 PM Grounded cond. ?  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Someone posed this ? to me.

Can someone land branch circuit neutrals onto a terminal in a separate enclosure and then continue the run back to the panel with a larger wire.

Assume the hots are run thru the same conduit.

I know its a weird question, but it was posed to me and I would like to make sure I quote the proper code that would not allow this.


2017 / 2014 NEC & Related Books and Study Guides

#81843 - 09/24/02 10:08 PM Re: Grounded cond. ?  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
You can if it is a "column" panel. See 300.3(B)(3). 225.7 and 215.4 would also permit a common neutral. What is the application involved in your question?
Don


Don(resqcapt19)

#81844 - 09/25/02 05:04 AM Re: Grounded cond. ?  
TE  Offline
Member
Joined: Aug 2002
Posts: 36
USA
I don't have time to look it up, but I seem to recall reading something to the effect
that the grounded conductors must return
to the panel of the un-grounded conductor
origin.

I guess in theory that method would be returning to the panel of origin.

With so many possibilities and code exceptions, as resqcapt says
What is the application specifically?


#81845 - 09/25/02 09:34 PM Re: Grounded cond. ?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Maybe 99NEC300-3. (b) Conductors of the Same Circuit—and—300-20. Induced Currents in Metal Enclosures or Metal Raceways.


#81846 - 09/26/02 06:31 PM Re: Grounded cond. ?  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
I have seen a "neutral block" installed in a 10x10 troff (wireway), the #12 & #10 neutrals terminated on the "block" and a #1 neutral from the "block" to the neutral bus in the panel.

I have also seen the same arrangement with grounds terminated at the troff, and a larger ground terminated at the panel.

The above jobs were inspected and approved
John


John

#81847 - 10/03/02 08:06 PM Re: Grounded cond. ?  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
This I believe was a typical residential service where the new panel was going to be in a new location. The contractor wanted to know if could use the existing neutral terminal and run one larger conductor from the old panel (which is now going to be gutted and used as a j-box) to the new panel, while carrying the hots for each of the existing circuits back to the new panel using separate conductors.

FYI-conduit is required in our municipality so separate cable runs are not a concern.


#81848 - 10/03/02 08:30 PM Re: Grounded cond. ?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Steve T

When will Chicago and some of the bedroom communities begin to allow other wiring methods such as "Romex or BX?"

What is the problem there?

Is it related to a concern over some older rules and political influence by the electrical inspectors?


Joe Tedesco, NEC Consultant

#81849 - 10/15/02 10:14 PM Re: Grounded cond. ?  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Joe,

I think you changed the topic, but just in case there is a correlation I missed...

Chicago is a strong union, steel manufacturing city. Fire statistics are supposedly low from electrical installations. (Not that I trust anyone's stats.) To answer your question, I doubt you'll see it unless a horribly corrupt union starts turning out unqualified electricians and problems start occuring.

I personally like the requirement because emt is a higher standard of installation than any type of cable. Additional circuit can be readily added or repaired or replaced with much less cost in the future.

EMT as an equipment grounding conductor is much more reliable than a wire over the long term life of an electrical system. Even BX that was allowed to be installed in Oak Park in the past is in many cases discovered with loose or disconnected connections. I see it every day. I constantly have to tell the electricians to tighten and secure BX connections that were "existing", when the back of bathroom, kitchen etc. walls get opened for a remodel.

I see much less old black pipe with loose connections. Also the walls did not have to get ripped open to replace the old cloth wiring.

If Romex was allowed, in my opinion, the number of non-code compliant, and severly dangerous installations would increase drastically in a period of 5 to 10 years.

I have worked in FL for a period of four years. The problems with electrical installations I saw in FL were more dangerous and much more costly to repair.

Of course, I grew up in Chicago and may have a biased opinion. Then again I may be completely objective.

Problem? Higher standards than the NEC is not a problem.


#81850 - 10/16/02 11:43 AM Re: Grounded cond. ?  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Oh by the way,

To date there have been almost 1200 electrical permits pulled this year alone in Oak Park. Oak Park has a population of about 60,000 and about 14,000 addresses. Having to run emt has not caused any type of slow down in construction.


#81851 - 10/16/02 04:18 PM Re: Grounded cond. ?  
Pearlfish  Offline
Member
Joined: Sep 2002
Posts: 83
Chicago Ridge, Il, USA
Here! Here! I couldn't agree with Steve more.



Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.8098 MB (Peak: 0.9871 MB) Zlib enabled. Server Time: 2017-10-18 09:15:37 UTC