ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
201 volt equipment?
by bigpapa. 04/29/17 12:15 AM
Schneider LC1D09
by jraef. 04/28/17 11:05 PM
Permit Snafus...AHJs and Contractors Jump in
by sparky. 04/28/17 08:11 PM
Electrode boilers question
by annemarie1. 04/27/17 01:40 PM
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,928 Are you busy
169,736 Re: Forum
162,951 Need opinion
Who's Online Now
0 registered members (), 36 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#81641 - 09/04/02 06:59 AM 1.5, 3, and 5kva transformer grounding.  
jlhmaint  Offline
Member
Joined: May 2002
Posts: 202
Fredericktown, OH, U.S.A
which section in the code will cover this and explain. please there are some different views at work and would like to clear this up. some are just hooking a ground to the metal case, others are tying X1 to ground and grounding the case. I have seen it done both ways or not at all. note these are typical 480V to 120 V

[This message has been edited by jlhmaint (edited 09-04-2002).]


2017 / 2014 NEC & Related Books and Study Guides

#81642 - 09/04/02 01:03 PM Re: 1.5, 3, and 5kva transformer grounding.  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
I can't quote code rules, as I do not know the NEC well enough, but the basic principles of grounding and bonding are similar everywhere.

The sketch below shows grounding and bonding for a typical single phase stepdown transformer.

[Linked Image]

Ed


#81643 - 09/04/02 02:57 PM Re: 1.5, 3, and 5kva transformer grounding.  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
These are Separately Derived Alternating-Current Systems as covered in 250.30. Eds drawing is right on the mark.
Don


Don(resqcapt19)

#81644 - 09/04/02 10:05 PM Re: 1.5, 3, and 5kva transformer grounding.  
jlhmaint  Offline
Member
Joined: May 2002
Posts: 202
Fredericktown, OH, U.S.A
ok that pic shows exactly how we do it in our building but we have seen some from our other building that were not like that or no ground or bond at all. Thanks


#81645 - 09/04/02 10:48 PM Re: 1.5, 3, and 5kva transformer grounding.  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
I may be missing something, but don't {99NEC} 250-30 and 250-26 fairly well cover the matter? The sizes listed are all above 1000VA. Probably one aspect of the ‘building steel’ versus “case” ground, it would seem more critical if the wiring runs extended out of a local area. [In the case of an open secondary bonding jumper, it’s maddening to have to do much troubleshooting on ungrounded 120V controls.]



Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 219
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7679 MB (Peak: 0.9062 MB) Zlib enabled. Server Time: 2017-04-29 11:30:22 UTC